    ... Heinz, I take your point. Batteries charged/discharged at 10% of their Ah rating have proven themselves (by 10% I mean that the maximum rate of
    Message 1 of 1 , Sep 19, 2001
    • 0 Attachment
      > From Heinz.Wenzl@...
      >
      > Some more comments on efficiency and use of batteries for spinning
      > reserve
      >
      > Andrew Tuckey wrote that batteries get destroyed very quickly if they
      > are used for spinning reserve applications where current fluctuates too much
      > and too quickly. Well it depends.
      >
      > The 17 MW/17MWh battery storage by BEWAG used for spinning reserve
      > applications in the Berlin grid achieved 7000 times the nominal capacity in
      > energy throughput. The daily capacity throughput was approx. 2.5 times the
      > nominal capacity.
      >
      > The battery was cooled, the electrolyte was stirred, single cells were
      > supervised and the battery was subjected to regular equalisation charges,
      > and the energy throughput happened in a partial state of charge. It was
      > extremely well designed. I do not see a reason why a smaller battery should
      > not achieve the same lifetime under similar conditions.

      Heinz,

      I take your point.

      Batteries charged/discharged at 10% of their Ah rating have proven themselves
      (by 10% I mean that the maximum rate of charge/discharge for a 100Ah battery
      is 10A so fully discharged in 10 hours).

      I gather from the above figures for the BEWAG battery storage, the batteries
      had the ability to be charged/discharged at 100% or their Ah rating. I.e. a
      17MW charge/discharge rate for a 17MW battery therefore fully discharged in 1
      hour.

      Well designed batteries can do this.

      However, for grid stability we are talking of discharging our "battery" from
      100% capacity to 25% capacity in 60 seconds or less. So we can exceed our
      nominal capacity in throughput in a number of minutes.

      With this time frame batteries do destroy themselves. Alternatively one could
      install a large enough battery so that the discharge rate is never more than
      some specific value (100% Ah rating) but the capital costs are prohibitive.

      We are using our system for grid stability; i.e. frequency control. This need
      only be done on a second by second basis, and we need only 60 seconds of
      energy reserve since we can bring other (Diesel) generators online in less
      than one minute.

      > Efficiency in/out is only one of the requirements of an energy storage
      > in renewable energy, the other is energy loss during standby-operation
      > when the energy is not required. It really depends on the installation
      > and the systems operation what is more important. Flywheels, for
      > instance, have a very high in/out efficiency but the losses (as a
      > percentage of energy stored) are extremely high - 100% per day or more.
      > With the high cost per kWh in renewable energy, these stand-by losses
      > can be crippling.

      I agree with all of that. I guess you could say we are using our system to
      store short-term power, not energy.

      Regards
      Andrew


      --
      Dr Andrew Tuckey
      Energy R&D Engineer
      Powercorp Pty. Ltd.
      Export Drive,
      Trade Development Zone
      Darwin, NT 0828
      Australia

      Phone: +61 8 8947 0933
      Fax: +61 8 8947 0925
      Web: www.pcorp.com.au
      Email: tuckey@...


      My deepest sympathy to the family and friends of the victims of the terrorist
      attacks, and to the whole of the USA.

      May the Lord comfort them.
    Your message has been successfully submitted and would be delivered to recipients shortly.