  • Kevin Hawkins
    Dec 1, 2012
    • 0 Attachment
      From what you say it's pretty difficult to determine if your gateway was ever receiving C-Bus status information.    What I'm slightly concerned about is that the gateway can't even read the C-Bus RS232 PCI configuration - regardless of being able to receive C-Bus information..    and I worry now that the current update may lock out your licences. 

      ISTR way back when you originally received the gateway you mentioned a similar issue and I created some newer firmware that improved the synch and that fixed it.  Did you update your gateway with those firmware builds and did it fix the issue for you then ?  I may be confusing this with someone else as we talked through C-Bus topology / burden issues and the latter would only be relevant if you were using a SIM (because Toolkit is working for you)..  Reagrdless it may be that a firmware update would fix this...

      Can you still do the exercise in letting me know if the gateway status page updates when you change something on C-Bus ..  You will need to use .Firefox or Chrome , not sure about Safari - might be OK.    IE doesn't work,as  it appends page updates.

      Where are you based - are you in the UK ?

        K



       On 01/12/2012 13:20, Ben Wilkinson wrote:
      Hi Kevin,
       
      Thanks again for your reply.
       
      I'm out at the moment, but have answered most of your questions below.

       

      I assume you still have the D: CB ID status and also there is still  SIM ID = 0  shown ?   

      >Yes, this was still the status this morning.

      Something has changed here because in this state there would be no communication from C-Bus at all , the gateway would not update HV so nothing in HV that depended on a C-Bus state change would have worked (which it was doing a  few days ago - or are you saying it wasn't ?).   Have you previously ever received status updates or triggered a macro in HV from C-Bus.

      > All I have used the gateway for until now is controlling Lights from HV.   That still works fine (ie I can obviously talk to CBus), including the new functionality of triggering scenes.  I haven't ever taken much notice of the status of the light screens, though have always had the feeling that it's not accurate.   I thought it was maintained in HV, so wasn't surprised.


      Have you physically moved the gateway at all in the last couple of days or re-configured C-Bus perhaps  - or loaded HV with some settings that mess up the custom lighting .. just before the issue started ?

      > No physical changes.   I have disconnected the Cbus PC interface a few times as I needed to programme it with toolit.

      Also - is the gateway visible on Ethernet (the xAP packets) ? 

      > Not sure about this.  Haven't done this for a while but will try later.

       Does the C-Bus RS232 interface work OK from C-Bus Toolkit ?

      > Everything seems to work fine in programming CBus from the toolkit.

      Your connections to the gateway sound OK.   The warning within the instructions is to not plug C-Bus i.e. the pink cable into the right hand (often grey) socket unless you have the C-Bus SIM installed on the gateway and the appropriate jumper settings changed.  This is because the higher voltage used on C-Bus will destroy the RS232 serial interface chip on the gateway.  Actually creating very similar symptoms to what you're seeing .....

      Your firmware is slightly older than current versions although I think that the issue you're seeing is more fundamental.    I know later versions had improved C-Bus synchronisation and maybe this could cause a misleading stop on stage D: CB ID.  But I'm loathe to get you to update the firmware as that just creates another possible unknown.  The licences are validated against the SIM ID's and so you could disable your gateway features if you update as there is no SIM ID being recovered.  The SIM ID is checked before any C-Bus messages.

      You say  " It also doesn’t show the status of any of the groups correctly (or at least very many of them).   " - If you have a group displaying a state here and you change that group on C-Bus (not from HV)  does it change state on the status web page  ?   

      >One the gateway web pages, for CBus it shows nearly all greyed out with occasional red dots.   Sometimes yellow.   They don't seem to be accurate at all and a bit random, but stays mostly greys.

      Virtual groups - i.e.  groups that HV changes will get updated on this status page by HV and not from the C-BUS status messages.   I'm trying to establish if any real groups, i.e. the ones present in C-Bus output units are getting updated on this page.   Were they updated previously OK ?

      >as far as I know, neither real (there are lots of them) or virtual are updated.

      Hope this helps a bit

      Ben 
          K






      01/12/2012 08:54, Ben Wilkinson wrote:

      Hi Kevin,

       

      I’ve done some physical checking this morning.   Wiring of the connector seems fine (checked with meter).   I’ve gone over the instructions again just to check everything physically is in the right place.   I’m plugging the HV into the LH socket (as you look at it) as per instructions.   The short CBus cable you made (for the CBus PCI) is plugged in the RH socket (grey).   I am a bit worried about the gateway instruction that says “ DO NOT PLUG C-BUS into this socket if you don’t have a SIM , the gateway or C-Bus could be damaged”

       

      As I don’t have a SIM, I wanted to be sure the RH socket is correct.   The previous line seems to say that I should plug it into this one.  

       

      I doubt that I’ve changed the jumpers, but I thought I should check them also.   This is JP5 with 6 header possibilities.   From the RHS (with pin 1 on LHS), jumpers are at pins 2, 3 and 4, with the jumpers on the pairs of pins further away from the socket.   Is this correct? 

       

      Ben

      From: ukusa_gateway@yahoogroups.com [mailto:ukusa_gateway@yahoogroups.com] On Behalf Of Ben Wilkinson
      Sent: 30 November 2012 18:55
      To: ukusa_gateway@yahoogroups.com
      Subject: RE: [ukusa_gateway] Taken a few steps backwards!

       

       

      HI Kevin,

       

      Thanks for the quick reply.   I am using the serial interface.   I have a feeling this might have been happening for some time as I can’t remember ever having seen the state of the CBus lights (although as I’ve never needed it until now, might have been there before).   All commands to the interface are working though (I did get the scene setting triggers working after I wrote first).   So I can control the whole CBus – just can’t see status of anything.   I’ll check the cables to the RS232, but I think they look good at least.

      &! nbsp;

      Ben

       

      From: ukusa_gateway@yahoogroups.com [mailto:ukusa_gateway@yahoogroups.com] On Behalf Of Kevin Hawkins
      Sent: 30 November 2012 17:47
      To: ukusa_gateway@yahoogroups.com
      Subject: Re: [ukusa_gateway] Taken a few steps backwards!

       

       

      The gateway is not able to see the C-Bus interface.    I can't remember if you have the onboard C-Bus SIM or are using a C-Bus RS232 serial interf a! ce  or maybe a C-Bus Ethernet interface.   Regardless t he C-Bus interface is not being found.  The first thing it does with C-Bus is to read the ID of the interface.    It will have completed it's HomeVision synchronisation but will be unable to see or control anything on C-Bus.    

      I'll assume you've power cycled the gateway a couple of times and it does the same ?

      This is likely caused by a physical change somewhere , probably in the cabling to the C-Bus RS232 interface or possibly  the C-Bus interface IP address being wrong if you're using an Ethernet interface (which I dont think you are).  if you're using an onboard SIM just check that it is seated correctly in it's socket.       

      K

      On 30/11/2012 16:37, Ben Wilkinson wrote:

      Hi Kevin,

       

      Things have gone a bit wrong today.   I’ve been trying to use the buttons on switches to perform additional actions (to the scene setting they’re already doing).   So that’s involved mapping the X10 actions to virtual CBus groups (which I then switch from within a scene).   I have tried many things but not getting it to work.   I think I’ve followed your Gateway instructions properly (I’ve certainly read it about 10 times!) but not having much joy.   One issue seems to be that the gateway status page doesn’t show “Running ok”.     It also doesn’t show the status of any of the groups correctly (or at least very many of them).  

       

      It shows: xAPRabbit : D: CB ID

       

      Then, underneath the matrix display of lights:

       

      Licence (xAP) CB HV MID:3268374032
      C-Bus SIM ID 0 SID:0 ver none
      Gateway ver beta 1 v22a 27th Jan 2009

       

      Also I now can’t seem to trigger scenes from HV like I could before.   The rest (old stuff) of the CBus light control is working fine. 

       

      Is there anything obvious I’m doing wrong you can tell ! from above message?

       

      Many thanks

       

      Ben

       

      From: ukusa_gateway@yahoogroups.com [mailto:ukusa_gateway@yahoogroups.com ] On Behalf Of Ben Wilkinson
      Sent: 26 November 2012 22:08
      To: ukusa_gateway@yahoo g! roups.com
      Subject: RE: [ukusa_gateway] Taken a few steps backwards!

       

       

      Thanks a lot for this Kevin.   As usual, tons of useful info!    I’m glad about the buffering.  I thought I’ve occasionally had lights not go on when a few were switched at a time.   But it’s unusual and I haven’t really taken much notice so may be mistaken.

       

      Useful reminder on the keys.   That had slipped my mind.   I think I’ll just use some sort of virtual group to indicate if a button has been pressed (assuming this is possible).   All I want to do in this ! circumstance is use it as an over-ride to automatic lighting so it should be fine.   Pity it doesn’t show which key has been presse d! though as then I might have been able to do some quite interesting things.

       

      Regards,

       

      Ben

       

      From: ukusa_gateway@yahoogroups.com [mailto:ukusa_gateway@yahoogroups.com] On Beh alf Of Kevin Hawkins
      Sent: 26 November 2012 14:35
      To: ukusa_gateway@yahoogroups.com
      Subject: Re: [ukusa_gateway] DLT and Saturn Scenes in the Gatew a! y

       

      < p class="MsoNormal"> 

      Glad it's working Ben -  best to avoid group 0 wherever possible I think.  BTW you can control all lighting compatible applications on C-Bus this way, there are quite a few of them....

      Scenes can be achieved either way - the approaches differ slightly however.

      If you implement a scene directly on C-Bus then it is totally independent of HV and the gateway.  The gateway does not know if a scene has been set or not although it does track every individual group change.  It is actioned f! aster because the intermediary steps via the serial port are not required and also the exact messages sent out on C-Bus are compacted better.   Scenes on C-Bus typically use the trigger application (202).    There is also a scene indicator possibility where a button light indicates the scene is set and all members are still in ! the correct state.  If one member group changes state this will be unset accordingly.  You can also spread scenes across scene capbale switches etc.  So if you had two DLT's  for example some of the scene can be held in one and the remainder in the other.   This will be your way around implementing large scenes Ben.

      If you implement a scene on HV then it has to be triggered via a group change on the lighting (56) application.  You can't use the trigger application.  A scene within HV is essentially a HV macro that runs when something changes (your scene set key) and so you can implement ! anything that HV is capable of including conditional logic, delays, le vel calculations etc. which can be really powerful.    IIRC in the current firmware you should now be able to send any sequence of lighting commands and not get buffer overflows as the messages  are concatenated correctly or split across separate C-Bus command s! as needed.   If that's not the case let me know.   ;   There is also no automatic maintainance of a 'scene valid' indicator within HV so you are not aware if a group within  your scene changes state, thus breaking the scene.   You could implement this via a macro if you wanted to know though.

      One thing just to clarify.....   pressing a key on C-Bus doesn't actually send a message at all.. only if a key is linked with a group do you see the command to change that group state go out.  You don't know where (which key) originated the message from within HV although it maybe shows in the xAP message (origin=).    Also a group onl y! maintains a state on C-Bus if it is present in an output unit e.g. a relay or dimmer.  If the group is not present in an output unit then it's called a virtual group.  Virtual groups are tracked by HV correctly so you can effectively treat them the same.  However an indicator light on C-Bus will not track the state of a virtual gro u! p and should you restart the gateway it will not be able to recover the current state of a virtual group from C-Bus. 