  • mechjackt
    I m using a .75kW 1140 RPM 3 phase induction motor in C-2C configuration as a generator. Calculations indicate cap values to be 20MF and 40MF. I find I have
    Message 1 of 2 , Mar 14, 2013
    • 0 Attachment
      I'm using a .75kW 1140 RPM 3 phase induction motor in C-2C configuration as a generator. Calculations indicate cap values to be 20MF and 40MF. I find I have to turn it at about 1800 RPM in order for it to excite. I tried temporarily connecting DC across 2 leads to induce magnetism but to no avail. When spinning at 1800 RPM the unloaded voltage is about 240V with frequency at over 100 HZ. With a 500W load voltage drops to about 165V, holding to 95 Hz. I've tried various capacitor values very little change in output. Any ideas how I can get 60 Hz at 240V with a 500 watt load?

      Thanks!
    • Nando
      I am attaching to this message the Nigel Smith notes Induction Motor as Generator Your motor 1140 RPM indicates that is a 6 pole motor rare for a 3/4 kw or
      Message 2 of 2 , Mar 15, 2013
      I am attaching to this message the Nigel Smith notes "Induction Motor as Generator"
       
      Your motor 1140 RPM indicates that is a 6 pole motor rare for a 3/4 kw  or 1 HP motor. it seems that it is a 4 pole since it energizes at 1800 RPM and the capacitors are wrong.
       
      I hope that your yahoo account accept an attachment of 7.1 MB otherwise send a message to me with a better email service.
       
      Nando
       
      ----- Original Message -----
      From: mechjackt
      Sent: Thursday, March 14, 2013 14:55
      Subject: [microhydro] induction generator problem

       

      I'm using a .75kW 1140 RPM 3 phase induction motor in C-2C configuration as a generator. Calculations indicate cap values to be 20MF and 40MF. I find I have to turn it at about 1800 RPM in order for it to excite. I tried temporarily connecting DC across 2 leads to induce magnetism but to no avail. When spinning at 1800 RPM the unloaded voltage is about 240V with frequency at over 100 HZ. With a 500W load voltage drops to about 165V, holding to 95 Hz. I've tried various capacitor values very little change in output. Any ideas how I can get 60 Hz at 240V with a 500 watt load?

      Thanks!