    I have had the same problem same wire (Igus). I normally have all my grounds coming back to the same point (star). I can t ground my motor cable shields or I
    Message 1 of 9 , Jul 26, 2013
    • 0 Attachment
      I have had the same problem same wire (Igus). I normally have all my grounds coming back to the same point (star). I can't ground my motor cable shields or I get a fault. I do have them terminated together but if I tie in the spindle shield I get the fault. I'm currently just shielding my spindle and not having a problem.
      Don

      Sent from Don Clifton's IPad

      On Jul 25, 2013, at 7:18 PM, qconvers@... wrote:

      > I'm still working on my noise problem. I'm getting there.
      >
      > If a gantry is only connected to the rest of the machine by the linear rail
      > blocks and you wanted to make a good earth between the two, how would you
      > do it without creating a ground loop?
      >
      > My stepper cables have an earth wire I've not used. Attach one end under a
      > stepper screw and the other at the star point in the control box... or run
      > a wire between gantry and table?
      >
      > Regards Dave
      >
      > [Non-text portions of this message have been removed]
      >
      >


      [Non-text portions of this message have been removed]
    • Andy Wander
      Just to clarify-the earth wire to your steppers-is it in fact a shield drain wire, or simply an unused conductor in the cable? If it s shied drain wire,
      Message 2 of 9 , Jul 26, 2013
      • 0 Attachment
        Just to clarify-the "earth wire" to your steppers-is it in fact a shield
        drain wire, or simply an unused conductor in the cable?



        If it's shied drain wire, then yes, it should be hooked up, at one end
        only, and the floating shield "may" have something to do with your problems.



        If it is just another conductor, then i doubt hooking it up will have any
        effect.



        Andy Wander

        _____

        From: mach1mach2cnc@yahoogroups.com [mailto:mach1mach2cnc@yahoogroups.com]
        On Behalf Of qconvers@...
        Sent: Friday, July 26, 2013 9:03 AM
        To: mach1mach2cnc@yahoogroups.com
        Subject: Re: [mach1mach2cnc] Re:noise problem. Update





        Thanks,

        So the rule is always back to the same point in the box.

        Is it known for stepper motors to suddenly become noisy?

        Regards Dave


        In a message dated 26/07/2013 13:49:16 GMT Daylight Time,
        cd.edwards@... <mailto:cd.edwards%40sasktel.net> writes:

        only attach one end of the shield. you would be better off attaching at
        the control box end though. Run a wire from the control box up and through
        to
        your gantry for your gantry ground. Don't rely on bearings to make your
        ground connections that would include linear guides etc.

        --- In mach1mach2cnc@yahoogroups.com
        <mailto:mach1mach2cnc%40yahoogroups.com> , qconvers@... wrote:
        >
        > I'm still working on my noise problem. I'm getting there.
        >
        > If a gantry is only connected to the rest of the machine by the linear
        rail
        > blocks and you wanted to make a good earth between the two, how would
        you
        > do it without creating a ground loop?
        >
        > My stepper cables have an earth wire I've not used. Attach one end under
        a
        > stepper screw and the other at the star point in the control box... or
        run
        > a wire between gantry and table?
        >
        > Regards Dave
        >
        > [Non-text portions of this message have been removed]
        >

        ------------------------------------

        www.machsupport.com - Web site AccessYahoo! Groups Links

        [Non-text portions of this message have been removed]





        [Non-text portions of this message have been removed]
      • quadconversions
        Hi Andy, it s a yellow/green wire within the shield with the other wires. My shields have always been grounded at one end in the control box. Regards Dave
        Message 3 of 9 , Jul 26, 2013
        • 0 Attachment
          Hi Andy,

          it's a yellow/green wire within the shield with the other wires. My
          shields have always been grounded at one end in the control box.

          Regards Dave


          In a message dated 26/07/2013 15:14:10 GMT Daylight Time,
          ohawiseguyeh@... writes:

          Just to clarify-the "earth wire" to your steppers-is it in fact a shield
          drain wire, or simply an unused conductor in the cable?



          If it's shied drain wire, then yes, it should be hooked up, at one end
          only, and the floating shield "may" have something to do with your
          problems.



          If it is just another conductor, then i doubt hooking it up will have any
          effect.



          Andy Wander

          _____

          From: mach1mach2cnc@yahoogroups.com [mailto:mach1mach2cnc@yahoogroups.com]
          On Behalf Of qconvers@...
          Sent: Friday, July 26, 2013 9:03 AM
          To: mach1mach2cnc@yahoogroups.com
          Subject: Re: [mach1mach2cnc] Re:noise problem. Update





          Thanks,

          So the rule is always back to the same point in the box.

          Is it known for stepper motors to suddenly become noisy?

          Regards Dave


          In a message dated 26/07/2013 13:49:16 GMT Daylight Time,
          cd.edwards@... <mailto:cd.edwards%40sasktel.net> writes:

          only attach one end of the shield. you would be better off attaching at
          the control box end though. Run a wire from the control box up and through
          to
          your gantry for your gantry ground. Don't rely on bearings to make your
          ground connections that would include linear guides etc.

          --- In mach1mach2cnc@yahoogroups.com
          <mailto:mach1mach2cnc%40yahoogroups.com> , qconvers@... wrote:
          >
          > I'm still working on my noise problem. I'm getting there.
          >
          > If a gantry is only connected to the rest of the machine by the linear
          rail
          > blocks and you wanted to make a good earth between the two, how would
          you
          > do it without creating a ground loop?
          >
          > My stepper cables have an earth wire I've not used. Attach one end under
          a
          > stepper screw and the other at the star point in the control box... or
          run
          > a wire between gantry and table?
          >
          > Regards Dave
          >
          > [Non-text portions of this message have been removed]
          >

          ------------------------------------

          www.machsupport.com - Web site AccessYahoo! Groups Links

          [Non-text portions of this message have been removed]





          [Non-text portions of this message have been removed]



          ------------------------------------

          www.machsupport.com - Web site AccessYahoo! Groups Links






          [Non-text portions of this message have been removed]
        • Andy Wander
          Well, it may be worth a shot to connect those wires to your star ground at one end, and to the motors frames at the other. Simple enough to do. I d them one at
          Message 4 of 9 , Jul 26, 2013
          • 0 Attachment
            Well, it may be worth a shot to connect those wires to your star ground at
            one end, and to the motors frames at the other. Simple enough to do. I'd
            them one at a time, and see what happens.



            I agree with the other poster that if it was working well, and then stopped
            working, as you describe, I'd be searching for a change, intentional or
            otherwise.



            Andy Wander

            _____

            From: mach1mach2cnc@yahoogroups.com [mailto:mach1mach2cnc@yahoogroups.com]
            On Behalf Of qconvers@...
            Sent: Friday, July 26, 2013 10:21 AM
            To: mach1mach2cnc@yahoogroups.com
            Subject: Re: [mach1mach2cnc] Re:noise problem. Update





            Hi Andy,

            it's a yellow/green wire within the shield with the other wires. My
            shields have always been grounded at one end in the control box.

            Regards Dave


            In a message dated 26/07/2013 15:14:10 GMT Daylight Time,
            ohawiseguyeh@... <mailto:ohawiseguyeh%40gmail.com> writes:

            Just to clarify-the "earth wire" to your steppers-is it in fact a shield
            drain wire, or simply an unused conductor in the cable?

            If it's shied drain wire, then yes, it should be hooked up, at one end
            only, and the floating shield "may" have something to do with your
            problems.

            If it is just another conductor, then i doubt hooking it up will have any
            effect.

            Andy Wander

            _____

            From: mach1mach2cnc@yahoogroups.com <mailto:mach1mach2cnc%40yahoogroups.com>
            [mailto:mach1mach2cnc@yahoogroups.com
            <mailto:mach1mach2cnc%40yahoogroups.com> ]
            On Behalf Of qconvers@... <mailto:qconvers%40aol.com>
            Sent: Friday, July 26, 2013 9:03 AM
            To: mach1mach2cnc@yahoogroups.com <mailto:mach1mach2cnc%40yahoogroups.com>
            Subject: Re: [mach1mach2cnc] Re:noise problem. Update

            Thanks,

            So the rule is always back to the same point in the box.

            Is it known for stepper motors to suddenly become noisy?

            Regards Dave

            In a message dated 26/07/2013 13:49:16 GMT Daylight Time,
            cd.edwards@... <mailto:cd.edwards%40sasktel.net>
            <mailto:cd.edwards%40sasktel.net> writes:

            only attach one end of the shield. you would be better off attaching at
            the control box end though. Run a wire from the control box up and through
            to
            your gantry for your gantry ground. Don't rely on bearings to make your
            ground connections that would include linear guides etc.

            --- In mach1mach2cnc@yahoogroups.com
            <mailto:mach1mach2cnc%40yahoogroups.com>
            <mailto:mach1mach2cnc%40yahoogroups.com> , qconvers@... wrote:
            >
            > I'm still working on my noise problem. I'm getting there.
            >
            > If a gantry is only connected to the rest of the machine by the linear
            rail
            > blocks and you wanted to make a good earth between the two, how would
            you
            > do it without creating a ground loop?
            >
            > My stepper cables have an earth wire I've not used. Attach one end under
            a
            > stepper screw and the other at the star point in the control box... or
            run
            > a wire between gantry and table?
            >
            > Regards Dave
            >
            > [Non-text portions of this message have been removed]
            >

            ------------------------------------

            www.machsupport.com - Web site AccessYahoo! Groups Links

            [Non-text portions of this message have been removed]

            [Non-text portions of this message have been removed]

            ------------------------------------

            www.machsupport.com - Web site AccessYahoo! Groups Links

            [Non-text portions of this message have been removed]





            [Non-text portions of this message have been removed]
          • quadconversions
            Hi Chuck, Yes, I took advice from this forum years ago and spared no expense in wires to do the job right. It s run good ever since.. until now. In a message
            Message 5 of 9 , Jul 26, 2013
            • 0 Attachment
              Hi Chuck,

              Yes, I took advice from this forum years ago and spared no expense in
              wires to do the job right. It's run good ever since.. until now.





              In a message dated 26/07/2013 15:14:20 GMT Daylight Time,
              chuckels@... writes:

              Dave,
              I seriously doubt that unless you made some major changes to the layout of
              configuration of your system that you developed a noise problem out of the
              blue.
              I would be more prone to look at wiring issues specifically broken or
              pinched.
              I know the electronic wizards on here are experts on noise and ground
              loops but you say your machine was running perfectly for a long time.
              Chuck

              ----- Original Message -----
              From: qconvers@...
              To: mach1mach2cnc@yahoogroups.com
              Sent: Friday, July 26, 2013 9:02 AM
              Subject: Re: [mach1mach2cnc] Re:noise problem. Update



              Thanks,

              So the rule is always back to the same point in the box.

              Is it known for stepper motors to suddenly become noisy?

              Regards Dave


              In a message dated 26/07/2013 13:49:16 GMT Daylight Time,
              cd.edwards@... writes:

              only attach one end of the shield. you would be better off attaching at
              the control box end though. Run a wire from the control box up and through
              to
              your gantry for your gantry ground. Don't rely on bearings to make your
              ground connections that would include linear guides etc.

              --- In mach1mach2cnc@yahoogroups.com, qconvers@... wrote:
              >
              > I'm still working on my noise problem. I'm getting there.
              >
              > If a gantry is only connected to the rest of the machine by the linear
              rail
              > blocks and you wanted to make a good earth between the two, how would
              you
              > do it without creating a ground loop?
              >
              > My stepper cables have an earth wire I've not used. Attach one end under
              a
              > stepper screw and the other at the star point in the control box... or
              run
              > a wire between gantry and table?
              >
              > Regards Dave
              >
              > [Non-text portions of this message have been removed]
              >

              ------------------------------------

              www.machsupport.com - Web site AccessYahoo! Groups Links

              [Non-text portions of this message have been removed]





              [Non-text portions of this message have been removed]



              ------------------------------------

              www.machsupport.com - Web site AccessYahoo! Groups Links






              [Non-text portions of this message have been removed]
            • chuck
              Dave, I seriously doubt that unless you made some major changes to the layout of configuration of your system that you developed a noise problem out of the
              Message 6 of 9 , Jul 26, 2013
              • 0 Attachment
                Dave,
                I seriously doubt that unless you made some major changes to the layout of configuration of your system that you developed a noise problem out of the blue.
                I would be more prone to look at wiring issues specifically broken or pinched.
                I know the electronic wizards on here are experts on noise and ground loops but you say your machine was running perfectly for a long time.
                Chuck

                ----- Original Message -----
                From: qconvers@...
                To: mach1mach2cnc@yahoogroups.com
                Sent: Friday, July 26, 2013 9:02 AM
                Subject: Re: [mach1mach2cnc] Re:noise problem. Update



                Thanks,

                So the rule is always back to the same point in the box.

                Is it known for stepper motors to suddenly become noisy?

                Regards Dave


                In a message dated 26/07/2013 13:49:16 GMT Daylight Time,
                cd.edwards@... writes:

                only attach one end of the shield. you would be better off attaching at
                the control box end though. Run a wire from the control box up and through to
                your gantry for your gantry ground. Don't rely on bearings to make your
                ground connections that would include linear guides etc.

                --- In mach1mach2cnc@yahoogroups.com, qconvers@... wrote:
                >
                > I'm still working on my noise problem. I'm getting there.
                >
                > If a gantry is only connected to the rest of the machine by the linear
                rail
                > blocks and you wanted to make a good earth between the two, how would
                you
                > do it without creating a ground loop?
                >
                > My stepper cables have an earth wire I've not used. Attach one end under
                a
                > stepper screw and the other at the star point in the control box... or
                run
                > a wire between gantry and table?
                >
                > Regards Dave
                >
                > [Non-text portions of this message have been removed]
                >

                ------------------------------------

                www.machsupport.com - Web site AccessYahoo! Groups Links

                [Non-text portions of this message have been removed]





                [Non-text portions of this message have been removed]
              Your message has been successfully submitted and would be delivered to recipients shortly.