Re: [engineeringcivil] minimum depth of backfill to be soil tested

Expand Messages
  • Mahesh B.L.
    Bernard, This should pose no problem. Perform a laboratory Modified Proctor Compaction Test to obtain the fill s MDD and OMC. Usually select fill is placed
    Message 1 of 12 , Aug 31, 2012
    View Source
    • 0 Attachment
      Bernard,

      This should pose no problem.  Perform a laboratory Modified Proctor Compaction Test to obtain the fill's MDD and OMC.  Usually "select fill" is placed below the foundations when required.  Place the fill in the pit excavated for foundation and compact it to 95% of its MDD in layers of 150mm until you reach your required founding level.  After completion, start placing your foundation concrete. 

      If your fill is not select fill, make sure to perform Atterberg limits test to ensure that the PI and limits are within the required limits.

      I hope the subsoil beneath the foundation is strong enough to take the designed loads from the columns!!

      Regards,
      Mahesh 

      On Sat, Sep 1, 2012 at 1:31 PM, BERNARD D <nard_gd@...> wrote:
       

      Dear all,

      What is the minimum depth of back-fill that is required to make soil test.
      i have only 250 to 300 mm back fill and the consultant told me to make a soil test before
      doing the small foundation of a 3.40m x 3,.40m AMR PANEL ROOM for a substation with 4 columns, 1 each corner and the foundation is 2meters by 2m by 300mm depth and the depth of footing is 1.50 meters from natural ground level. the subcontractor excavated too much, 1.80 meters thats why we make 300mm backfill.
      Guys, i need your opinion with this.

      Thank you very much.


      Best regards,

      BERNARD


    • Mahesh B.L.
      Bernard, This should pose no problem. Perform a laboratory Modified Proctor Compaction Test to obtain the fill s MDD and OMC. Usually select fill is placed
      Message 2 of 12 , Aug 31, 2012
      View Source
      • 0 Attachment
        Bernard,

        This should pose no problem.  Perform a laboratory Modified Proctor Compaction Test to obtain the fill's MDD and OMC.  Usually "select fill" is placed below the foundations when required.  Place the fill in the pit excavated for foundation and compact it to 95% of its MDD in layers of 150mm until you reach your required founding level.  After completion, start placing your foundation concrete. 

        If your fill is not select fill, make sure to perform Atterberg limits test to ensure that the PI and limits are within the required limits.

        I hope the subsoil beneath the foundation is strong enough to take the designed loads from the columns!!

        Regards,
        Mahesh 

        On Sat, Sep 1, 2012 at 1:31 PM, BERNARD D <nard_gd@...> wrote:
         

        Dear all,

        What is the minimum depth of back-fill that is required to make soil test.
        i have only 250 to 300 mm back fill and the consultant told me to make a soil test before
        doing the small foundation of a 3.40m x 3,.40m AMR PANEL ROOM for a substation with 4 columns, 1 each corner and the foundation is 2meters by 2m by 300mm depth and the depth of footing is 1.50 meters from natural ground level. the subcontractor excavated too much, 1.80 meters thats why we make 300mm backfill.
        Guys, i need your opinion with this.

        Thank you very much.


        Best regards,

        BERNARD


      • sakthi vel
        Hi Back filling Generally 200 mm Back fill because core Test mould 200 mm . every layer fill 250 mm lay and compact take core and determine compaction This is
        Message 3 of 12 , Sep 1, 2012
        View Source
        • 0 Attachment
          Hi
           
           
            Back filling
           
              Generally 200 mm Back fill because core Test mould 200 mm . every layer fill 250 mm lay and compact take core and determine compaction This is the method back filling

          On Sat, Sep 1, 2012 at 12:20 PM, Mahesh B.L. <geo.mahesh@...> wrote:
           

          Bernard,

          This should pose no problem.  Perform a laboratory Modified Proctor Compaction Test to obtain the fill's MDD and OMC.  Usually "select fill" is placed below the foundations when required.  Place the fill in the pit excavated for foundation and compact it to 95% of its MDD in layers of 150mm until you reach your required founding level.  After completion, start placing your foundation concrete. 

          If your fill is not select fill, make sure to perform Atterberg limits test to ensure that the PI and limits are within the required limits.

          I hope the subsoil beneath the foundation is strong enough to take the designed loads from the columns!!

          Regards,
          Mahesh 

          On Sat, Sep 1, 2012 at 1:31 PM, BERNARD D <nard_gd@...> wrote:
           

          Dear all,

          What is the minimum depth of back-fill that is required to make soil test.
          i have only 250 to 300 mm back fill and the consultant told me to make a soil test before
          doing the small foundation of a 3.40m x 3,.40m AMR PANEL ROOM for a substation with 4 columns, 1 each corner and the foundation is 2meters by 2m by 300mm depth and the depth of footing is 1.50 meters from natural ground level. the subcontractor excavated too much, 1.80 meters thats why we make 300mm backfill.
          Guys, i need your opinion with this.

          Thank you very much.


          Best regards,

          BERNARD



        • BERNARD D
          Hello Engr. Mahesh, Thanks a lot for your reply. Yes the natural soil beneth the foundation is adobe and its really strong enought to hold the foundation of a
          Message 4 of 12 , Sep 2, 2012
          View Source
          • 0 Attachment
            Hello Engr. Mahesh,

            Thanks a lot for your reply. Yes the natural soil beneth the foundation is adobe and its really strong enought to hold the foundation of a small room for 2 AMR (Automatic Meter Reading) Panels connected to a substation.
            I was just convincing the consultant that no need to make laboratory soil test because its only a small room and its costly and time consuming to make soil test. and i assure them that we backfill and ccompact it according to the correct method and specification.


            Bernard

            --- On Sat, 9/1/12, sakthi vel <sweetheart.vel@...> wrote:

            From: sakthi vel <sweetheart.vel@...>
            Subject: Re: [engineeringcivil] minimum depth of backfill to be soil tested
            To: engineeringcivil@yahoogroups.com
            Date: Saturday, September 1, 2012, 9:28 AM

             

            Hi
             
             
              Back filling
             
                Generally 200 mm Back fill because core Test mould 200 mm . every layer fill 250 mm lay and compact take core and determine compaction This is the method back filling

            On Sat, Sep 1, 2012 at 12:20 PM, Mahesh B.L. <geo.mahesh@...> wrote:
             

            Bernard,

            This should pose no problem.  Perform a laboratory Modified Proctor Compaction Test to obtain the fill's MDD and OMC.  Usually "select fill" is placed below the foundations when required.  Place the fill in the pit excavated for foundation and compact it to 95% of its MDD in layers of 150mm until you reach your required founding level.  After completion, start placing your foundation concrete. 

            If your fill is not select fill, make sure to perform Atterberg limits test to ensure that the PI and limits are within the required limits.

            I hope the subsoil beneath the foundation is strong enough to take the designed loads from the columns!!

            Regards,
            Mahesh 

            On Sat, Sep 1, 2012 at 1:31 PM, BERNARD D <nard_gd@...> wrote:
             

            Dear all,

            What is the minimum depth of back-fill that is required to make soil test.
            i have only 250 to 300 mm back fill and the consultant told me to make a soil test before
            doing the small foundation of a 3.40m x 3,.40m AMR PANEL ROOM for a substation with 4 columns, 1 each corner and the foundation is 2meters by 2m by 300mm depth and the depth of footing is 1.50 meters from natural ground level. the subcontractor excavated too much, 1.80 meters thats why we make 300mm backfill.
            Guys, i need your opinion with this.

            Thank you very much.


            Best regards,

            BERNARD



          • Mahesh B.L.
            Bernard, I understand your problem. But I presume to obtain the laboratory test results, it may hardly take 2-3 days from the day you provide the sample to a
            Message 5 of 12 , Sep 2, 2012
            View Source
            • 0 Attachment
              Bernard, 

              I understand your problem.  But I presume to obtain the laboratory test results, it may hardly take 2-3 days from the day you provide the sample to a soil laboratory and they start the work immediately on it.

              If the client says it is to be done and if it is in the contract between you and your client, then I think we ought to respect the engineering ethics. 

              Go ahead, all the best.

              Regards,
              Mahesh

              On Sun, Sep 2, 2012 at 6:00 PM, BERNARD D <nard_gd@...> wrote:
               

              Hello Engr. Mahesh,

              Thanks a lot for your reply. Yes the natural soil beneth the foundation is adobe and its really strong enought to hold the foundation of a small room for 2 AMR (Automatic Meter Reading) Panels connected to a substation.
              I was just convincing the consultant that no need to make laboratory soil test because its only a small room and its costly and time consuming to make soil test. and i assure them that we backfill and ccompact it according to the correct method and specification.


              Bernard

              --- On Sat, 9/1/12, sakthi vel <sweetheart.vel@...> wrote:

              From: sakthi vel <sweetheart.vel@...>
              Subject: Re: [engineeringcivil] minimum depth of backfill to be soil tested
              To: engineeringcivil@yahoogroups.com
              Date: Saturday, September 1, 2012, 9:28 AM


               

              Hi
               
               
                Back filling
               
                  Generally 200 mm Back fill because core Test mould 200 mm . every layer fill 250 mm lay and compact take core and determine compaction This is the method back filling

              On Sat, Sep 1, 2012 at 12:20 PM, Mahesh B.L. <geo.mahesh@...> wrote:
               

              Bernard,

              This should pose no problem.  Perform a laboratory Modified Proctor Compaction Test to obtain the fill's MDD and OMC.  Usually "select fill" is placed below the foundations when required.  Place the fill in the pit excavated for foundation and compact it to 95% of its MDD in layers of 150mm until you reach your required founding level.  After completion, start placing your foundation concrete. 

              If your fill is not select fill, make sure to perform Atterberg limits test to ensure that the PI and limits are within the required limits.

              I hope the subsoil beneath the foundation is strong enough to take the designed loads from the columns!!

              Regards,
              Mahesh 

              On Sat, Sep 1, 2012 at 1:31 PM, BERNARD D <nard_gd@...> wrote:
               

              Dear all,

              What is the minimum depth of back-fill that is required to make soil test.
              i have only 250 to 300 mm back fill and the consultant told me to make a soil test before
              doing the small foundation of a 3.40m x 3,.40m AMR PANEL ROOM for a substation with 4 columns, 1 each corner and the foundation is 2meters by 2m by 300mm depth and the depth of footing is 1.50 meters from natural ground level. the subcontractor excavated too much, 1.80 meters thats why we make 300mm backfill.
              Guys, i need your opinion with this.

              Thank you very much.


              Best regards,

              BERNARD




            • BERNARD D
              yes you are right engineer Mahesh. i should respect engineering ethics.and its also safer for my side. thanks a lot for your concerned and support. God bless u
              Message 6 of 12 , Sep 4, 2012
              View Source
              • 0 Attachment
                yes you are right engineer Mahesh. i should respect engineering ethics.and its also safer for my side. thanks a lot for your concerned and support. God bless u more..

                regards,

                Bernard

                --- On Sun, 9/2/12, Mahesh B.L. <geo.mahesh@...> wrote:

                From: Mahesh B.L. <geo.mahesh@...>
                Subject: Re: [engineeringcivil] minimum depth of backfill to be soil tested
                To: engineeringcivil@yahoogroups.com
                Date: Sunday, September 2, 2012, 4:54 AM

                 

                Bernard, 


                I understand your problem.  But I presume to obtain the laboratory test results, it may hardly take 2-3 days from the day you provide the sample to a soil laboratory and they start the work immediately on it.

                If the client says it is to be done and if it is in the contract between you and your client, then I think we ought to respect the engineering ethics. 

                Go ahead, all the best.

                Regards,
                Mahesh

                On Sun, Sep 2, 2012 at 6:00 PM, BERNARD D <nard_gd@...> wrote:
                 

                Hello Engr. Mahesh,

                Thanks a lot for your reply. Yes the natural soil beneth the foundation is adobe and its really strong enought to hold the foundation of a small room for 2 AMR (Automatic Meter Reading) Panels connected to a substation.
                I was just convincing the consultant that no need to make laboratory soil test because its only a small room and its costly and time consuming to make soil test. and i assure them that we backfill and ccompact it according to the correct method and specification.


                Bernard

                --- On Sat, 9/1/12, sakthi vel <sweetheart.vel@...> wrote:

                From: sakthi vel <sweetheart.vel@...>
                Subject: Re: [engineeringcivil] minimum depth of backfill to be soil tested
                To: engineeringcivil@yahoogroups.com
                Date: Saturday, September 1, 2012, 9:28 AM


                 

                Hi
                 
                 
                  Back filling
                 
                    Generally 200 mm Back fill because core Test mould 200 mm . every layer fill 250 mm lay and compact take core and determine compaction This is the method back filling

                On Sat, Sep 1, 2012 at 12:20 PM, Mahesh B.L. <geo.mahesh@...> wrote:
                 

                Bernard,

                This should pose no problem.  Perform a laboratory Modified Proctor Compaction Test to obtain the fill's MDD and OMC.  Usually "select fill" is placed below the foundations when required.  Place the fill in the pit excavated for foundation and compact it to 95% of its MDD in layers of 150mm until you reach your required founding level.  After completion, start placing your foundation concrete. 

                If your fill is not select fill, make sure to perform Atterberg limits test to ensure that the PI and limits are within the required limits.

                I hope the subsoil beneath the foundation is strong enough to take the designed loads from the columns!!

                Regards,
                Mahesh 

                On Sat, Sep 1, 2012 at 1:31 PM, BERNARD D <nard_gd@...> wrote:
                 

                Dear all,

                What is the minimum depth of back-fill that is required to make soil test.
                i have only 250 to 300 mm back fill and the consultant told me to make a soil test before
                doing the small foundation of a 3.40m x 3,.40m AMR PANEL ROOM for a substation with 4 columns, 1 each corner and the foundation is 2meters by 2m by 300mm depth and the depth of footing is 1.50 meters from natural ground level. the subcontractor excavated too much, 1.80 meters thats why we make 300mm backfill.
                Guys, i need your opinion with this.

                Thank you very much.


                Best regards,

                BERNARD




              • BERNARD D
                yes you are right engineer Mahesh. i should respect engineering ethics.and its also safer for my side. thanks a lot for your concerned and support. God bless u
                Message 7 of 12 , Sep 4, 2012
                View Source
                • 0 Attachment
                  yes you are right engineer Mahesh. i should respect engineering ethics.and its also safer for my side. thanks a lot for your concerned and support. God bless u more..

                  regards,

                  Bernard

                  --- On Sun, 9/2/12, Mahesh B.L. <geo.mahesh@...> wrote:

                  From: Mahesh B.L. <geo.mahesh@...>
                  Subject: Re: [engineeringcivil] minimum depth of backfill to be soil tested
                  To: engineeringcivil@yahoogroups.com
                  Date: Sunday, September 2, 2012, 4:54 AM

                   

                  Bernard, 


                  I understand your problem.  But I presume to obtain the laboratory test results, it may hardly take 2-3 days from the day you provide the sample to a soil laboratory and they start the work immediately on it.

                  If the client says it is to be done and if it is in the contract between you and your client, then I think we ought to respect the engineering ethics. 

                  Go ahead, all the best.

                  Regards,
                  Mahesh

                  On Sun, Sep 2, 2012 at 6:00 PM, BERNARD D <nard_gd@...> wrote:
                   

                  Hello Engr. Mahesh,

                  Thanks a lot for your reply. Yes the natural soil beneth the foundation is adobe and its really strong enought to hold the foundation of a small room for 2 AMR (Automatic Meter Reading) Panels connected to a substation.
                  I was just convincing the consultant that no need to make laboratory soil test because its only a small room and its costly and time consuming to make soil test. and i assure them that we backfill and ccompact it according to the correct method and specification.


                  Bernard

                  --- On Sat, 9/1/12, sakthi vel <sweetheart.vel@...> wrote:

                  From: sakthi vel <sweetheart.vel@...>
                  Subject: Re: [engineeringcivil] minimum depth of backfill to be soil tested
                  To: engineeringcivil@yahoogroups.com
                  Date: Saturday, September 1, 2012, 9:28 AM


                   

                  Hi
                   
                   
                    Back filling
                   
                      Generally 200 mm Back fill because core Test mould 200 mm . every layer fill 250 mm lay and compact take core and determine compaction This is the method back filling

                  On Sat, Sep 1, 2012 at 12:20 PM, Mahesh B.L. <geo.mahesh@...> wrote:
                   

                  Bernard,

                  This should pose no problem.  Perform a laboratory Modified Proctor Compaction Test to obtain the fill's MDD and OMC.  Usually "select fill" is placed below the foundations when required.  Place the fill in the pit excavated for foundation and compact it to 95% of its MDD in layers of 150mm until you reach your required founding level.  After completion, start placing your foundation concrete. 

                  If your fill is not select fill, make sure to perform Atterberg limits test to ensure that the PI and limits are within the required limits.

                  I hope the subsoil beneath the foundation is strong enough to take the designed loads from the columns!!

                  Regards,
                  Mahesh 

                  On Sat, Sep 1, 2012 at 1:31 PM, BERNARD D <nard_gd@...> wrote:
                   

                  Dear all,

                  What is the minimum depth of back-fill that is required to make soil test.
                  i have only 250 to 300 mm back fill and the consultant told me to make a soil test before
                  doing the small foundation of a 3.40m x 3,.40m AMR PANEL ROOM for a substation with 4 columns, 1 each corner and the foundation is 2meters by 2m by 300mm depth and the depth of footing is 1.50 meters from natural ground level. the subcontractor excavated too much, 1.80 meters thats why we make 300mm backfill.
                  Guys, i need your opinion with this.

                  Thank you very much.


                  Best regards,

                  BERNARD




                • satish tumne
                  dear,  In many cases contract says to fill up this extra excavation by means of concrete and it is at the cost of contractor. to get earth filling tested for
                  Message 8 of 12 , Sep 4, 2012
                  View Source
                  • 0 Attachment
                    dear,
                     In many cases contract says to fill up this extra excavation by means of concrete and it is at the cost of contractor.
                    to get earth filling tested for compression is easy way out
                    thanks
                    Satish Tumne


                    From: BERNARD D <nard_gd@...>
                    To: engineeringcivil@yahoogroups.com
                    Sent: Tuesday, September 4, 2012 1:45 PM
                    Subject: Re: [engineeringcivil] minimum depth of backfill to be soil tested



                    yes you are right engineer Mahesh. i should respect engineering ethics.and its also safer for my side. thanks a lot for your concerned and support. God bless u more..

                    regards,

                    Bernard

                    --- On Sun, 9/2/12, Mahesh B.L. <geo.mahesh@...> wrote:

                    From: Mahesh B.L. <geo.mahesh@...>
                    Subject: Re: [engineeringcivil] minimum depth of backfill to be soil tested
                    To: engineeringcivil@yahoogroups.com
                    Date: Sunday, September 2, 2012, 4:54 AM

                     
                    Bernard, 

                    I understand your problem.  But I presume to obtain the laboratory test results, it may hardly take 2-3 days from the day you provide the sample to a soil laboratory and they start the work immediately on it.

                    If the client says it is to be done and if it is in the contract between you and your client, then I think we ought to respect the engineering ethics. 

                    Go ahead, all the best.

                    Regards,
                    Mahesh

                    On Sun, Sep 2, 2012 at 6:00 PM, BERNARD D <nard_gd@...> wrote:
                     
                    Hello Engr. Mahesh,

                    Thanks a lot for your reply. Yes the natural soil beneth the foundation is adobe and its really strong enought to hold the foundation of a small room for 2 AMR (Automatic Meter Reading) Panels connected to a substation.
                    I was just convincing the consultant that no need to make laboratory soil test because its only a small room and its costly and time consuming to make soil test. and i assure them that we backfill and ccompact it according to the correct method and specification.


                    Bernard

                    --- On Sat, 9/1/12, sakthi vel <sweetheart.vel@...> wrote:

                    From: sakthi vel <sweetheart.vel@...>
                    Subject: Re: [engineeringcivil] minimum depth of backfill to be soil tested
                    To: engineeringcivil@yahoogroups.com
                    Date: Saturday, September 1, 2012, 9:28 AM


                     
                    Hi
                     
                     
                      Back filling
                     
                        Generally 200 mm Back fill because core Test mould 200 mm . every layer fill 250 mm lay and compact take core and determine compaction This is the method back filling

                    On Sat, Sep 1, 2012 at 12:20 PM, Mahesh B.L. <geo.mahesh@...> wrote:
                     
                    Bernard,

                    This should pose no problem.  Perform a laboratory Modified Proctor Compaction Test to obtain the fill's MDD and OMC.  Usually "select fill" is placed below the foundations when required.  Place the fill in the pit excavated for foundation and compact it to 95% of its MDD in layers of 150mm until you reach your required founding level.  After completion, start placing your foundation concrete. 

                    If your fill is not select fill, make sure to perform Atterberg limits test to ensure that the PI and limits are within the required limits.

                    I hope the subsoil beneath the foundation is strong enough to take the designed loads from the columns!!

                    Regards,
                    Mahesh 

                    On Sat, Sep 1, 2012 at 1:31 PM, BERNARD D <nard_gd@...> wrote:
                     
                    Dear all,

                    What is the minimum depth of back-fill that is required to make soil test.
                    i have only 250 to 300 mm back fill and the consultant told me to make a soil test before
                    doing the small foundation of a 3.40m x 3,.40m AMR PANEL ROOM for a substation with 4 columns, 1 each corner and the foundation is 2meters by 2m by 300mm depth and the depth of footing is 1.50 meters from natural ground level. the subcontractor excavated too much, 1.80 meters thats why we make 300mm backfill.
                    Guys, i need your opinion with this.

                    Thank you very much.


                    Best regards,

                    BERNARD








                  • BERNARD D
                    Thank you Mr. Satish,  but 300mm thick concrete as fill for over excavation is costly so i would rather backfill with suitable soil and backfill and make
                    Message 9 of 12 , Sep 4, 2012
                    View Source
                    • 0 Attachment
                      Thank you Mr. Satish,  but 300mm thick concrete as fill for over excavation is costly so i would rather backfill with suitable soil and backfill and make compaction test.


                      From: satish tumne <tumne@...>
                      To: "engineeringcivil@yahoogroups.com" <engineeringcivil@yahoogroups.com>
                      Sent: Tuesday, September 4, 2012 1:29 PM
                      Subject: Re: [engineeringcivil] minimum depth of backfill to be soil tested

                       
                      dear,
                       In many cases contract says to fill up this extra excavation by means of concrete and it is at the cost of contractor.
                      to get earth filling tested for compression is easy way out
                      thanks
                      Satish Tumne


                      From: BERNARD D <nard_gd@...>
                      To: engineeringcivil@yahoogroups.com
                      Sent: Tuesday, September 4, 2012 1:45 PM
                      Subject: Re: [engineeringcivil] minimum depth of backfill to be soil tested



                      yes you are right engineer Mahesh. i should respect engineering ethics.and its also safer for my side. thanks a lot for your concerned and support. God bless u more..

                      regards,

                      Bernard

                      --- On Sun, 9/2/12, Mahesh B.L. <geo.mahesh@...> wrote:

                      From: Mahesh B.L. <geo.mahesh@...>
                      Subject: Re: [engineeringcivil] minimum depth of backfill to be soil tested
                      To: engineeringcivil@yahoogroups.com
                      Date: Sunday, September 2, 2012, 4:54 AM

                       
                      Bernard, 

                      I understand your problem.  But I presume to obtain the laboratory test results, it may hardly take 2-3 days from the day you provide the sample to a soil laboratory and they start the work immediately on it.

                      If the client says it is to be done and if it is in the contract between you and your client, then I think we ought to respect the engineering ethics. 

                      Go ahead, all the best.

                      Regards,
                      Mahesh

                      On Sun, Sep 2, 2012 at 6:00 PM, BERNARD D <nard_gd@...> wrote:
                       
                      Hello Engr. Mahesh,

                      Thanks a lot for your reply. Yes the natural soil beneth the foundation is adobe and its really strong enought to hold the foundation of a small room for 2 AMR (Automatic Meter Reading) Panels connected to a substation.
                      I was just convincing the consultant that no need to make laboratory soil test because its only a small room and its costly and time consuming to make soil test. and i assure them that we backfill and ccompact it according to the correct method and specification.


                      Bernard

                      --- On Sat, 9/1/12, sakthi vel <sweetheart.vel@...> wrote:

                      From: sakthi vel <sweetheart.vel@...>
                      Subject: Re: [engineeringcivil] minimum depth of backfill to be soil tested
                      To: engineeringcivil@yahoogroups.com
                      Date: Saturday, September 1, 2012, 9:28 AM


                       
                      Hi
                       
                       
                        Back filling
                       
                          Generally 200 mm Back fill because core Test mould 200 mm . every layer fill 250 mm lay and compact take core and determine compaction This is the method back filling

                      On Sat, Sep 1, 2012 at 12:20 PM, Mahesh B.L. <geo.mahesh@...> wrote:
                       
                      Bernard,

                      This should pose no problem.  Perform a laboratory Modified Proctor Compaction Test to obtain the fill's MDD and OMC.  Usually "select fill" is placed below the foundations when required.  Place the fill in the pit excavated for foundation and compact it to 95% of its MDD in layers of 150mm until you reach your required founding level.  After completion, start placing your foundation concrete. 

                      If your fill is not select fill, make sure to perform Atterberg limits test to ensure that the PI and limits are within the required limits.

                      I hope the subsoil beneath the foundation is strong enough to take the designed loads from the columns!!

                      Regards,
                      Mahesh 

                      On Sat, Sep 1, 2012 at 1:31 PM, BERNARD D <nard_gd@...> wrote:
                       
                      Dear all,

                      What is the minimum depth of back-fill that is required to make soil test.
                      i have only 250 to 300 mm back fill and the consultant told me to make a soil test before
                      doing the small foundation of a 3.40m x 3,.40m AMR PANEL ROOM for a substation with 4 columns, 1 each corner and the foundation is 2meters by 2m by 300mm depth and the depth of footing is 1.50 meters from natural ground level. the subcontractor excavated too much, 1.80 meters thats why we make 300mm backfill.
                      Guys, i need your opinion with this.

                      Thank you very much.


                      Best regards,

                      BERNARD










                    • Sujit Dhital
                      fill the over excavated foundation with suitable back fill material and get its field density and copare with the MDD at lab . its more than 95% the compaction
                      Message 10 of 12 , Oct 12, 2012
                      View Source
                      • 0 Attachment
                        fill the over excavated foundation with suitable back fill material and get its field density and copare with the MDD at lab . its more than 95% the compaction is ok go for further works .
                         
                        Sujit Dhital


                        From: BERNARD D <nard_gd@...>
                        To: "engineeringcivil@yahoogroups.com" <engineeringcivil@yahoogroups.com>
                        Sent: Tuesday, September 4, 2012 5:36 PM
                        Subject: Re: [engineeringcivil] minimum depth of backfill to be soil tested

                         
                        Thank you Mr. Satish,  but 300mm thick concrete as fill for over excavation is costly so i would rather backfill with suitable soil and backfill and make compaction test.


                        From: satish tumne <tumne@...>
                        To: "engineeringcivil@yahoogroups.com" <engineeringcivil@yahoogroups.com>
                        Sent: Tuesday, September 4, 2012 1:29 PM
                        Subject: Re: [engineeringcivil] minimum depth of backfill to be soil tested

                         
                        dear,
                         In many cases contract says to fill up this extra excavation by means of concrete and it is at the cost of contractor.
                        to get earth filling tested for compression is easy way out
                        thanks
                        Satish Tumne


                        From: BERNARD D <nard_gd@...>
                        To: engineeringcivil@yahoogroups.com
                        Sent: Tuesday, September 4, 2012 1:45 PM
                        Subject: Re: [engineeringcivil] minimum depth of backfill to be soil tested



                        yes you are right engineer Mahesh. i should respect engineering ethics.and its also safer for my side. thanks a lot for your concerned and support. God bless u more..

                        regards,

                        Bernard

                        --- On Sun, 9/2/12, Mahesh B.L. <geo.mahesh@...> wrote:

                        From: Mahesh B.L. <geo.mahesh@...>
                        Subject: Re: [engineeringcivil] minimum depth of backfill to be soil tested
                        To: engineeringcivil@yahoogroups.com
                        Date: Sunday, September 2, 2012, 4:54 AM

                         
                        Bernard, 

                        I understand your problem.  But I presume to obtain the laboratory test results, it may hardly take 2-3 days from the day you provide the sample to a soil laboratory and they start the work immediately on it.

                        If the client says it is to be done and if it is in the contract between you and your client, then I think we ought to respect the engineering ethics. 

                        Go ahead, all the best.

                        Regards,
                        Mahesh

                        On Sun, Sep 2, 2012 at 6:00 PM, BERNARD D <nard_gd@...> wrote:
                         
                        Hello Engr. Mahesh,

                        Thanks a lot for your reply. Yes the natural soil beneth the foundation is adobe and its really strong enought to hold the foundation of a small room for 2 AMR (Automatic Meter Reading) Panels connected to a substation.
                        I was just convincing the consultant that no need to make laboratory soil test because its only a small room and its costly and time consuming to make soil test. and i assure them that we backfill and ccompact it according to the correct method and specification.


                        Bernard

                        --- On Sat, 9/1/12, sakthi vel <sweetheart.vel@...> wrote:

                        From: sakthi vel <sweetheart.vel@...>
                        Subject: Re: [engineeringcivil] minimum depth of backfill to be soil tested
                        To: engineeringcivil@yahoogroups.com
                        Date: Saturday, September 1, 2012, 9:28 AM


                         
                        Hi
                         
                         
                          Back filling
                         
                            Generally 200 mm Back fill because core Test mould 200 mm . every layer fill 250 mm lay and compact take core and determine compaction This is the method back filling

                        On Sat, Sep 1, 2012 at 12:20 PM, Mahesh B.L. <geo.mahesh@...> wrote:
                         
                        Bernard,

                        This should pose no problem.  Perform a laboratory Modified Proctor Compaction Test to obtain the fill's MDD and OMC.  Usually "select fill" is placed below the foundations when required.  Place the fill in the pit excavated for foundation and compact it to 95% of its MDD in layers of 150mm until you reach your required founding level.  After completion, start placing your foundation concrete. 

                        If your fill is not select fill, make sure to perform Atterberg limits test to ensure that the PI and limits are within the required limits.

                        I hope the subsoil beneath the foundation is strong enough to take the designed loads from the columns!!

                        Regards,
                        Mahesh 

                        On Sat, Sep 1, 2012 at 1:31 PM, BERNARD D <nard_gd@...> wrote:
                         
                        Dear all,

                        What is the minimum depth of back-fill that is required to make soil test.
                        i have only 250 to 300 mm back fill and the consultant told me to make a soil test before
                        doing the small foundation of a 3.40m x 3,.40m AMR PANEL ROOM for a substation with 4 columns, 1 each corner and the foundation is 2meters by 2m by 300mm depth and the depth of footing is 1.50 meters from natural ground level. the subcontractor excavated too much, 1.80 meters thats why we make 300mm backfill.
                        Guys, i need your opinion with this.

                        Thank you very much.


                        Best regards,

                        BERNARD