  • coy13gov
    Still lovin the site. Yes agree with all on the generators. OMG! cant imagine getting a larger one,and Yes on b careful on the surge power as some of the
    Message 1 of 13 , Nov 17, 2012
      Still lovin' the site. Yes agree with all on the generators. OMG! cant imagine getting a larger one,and Yes on b careful on the "surge" power as some of the other guys talk. TO me think on really your demand.
      On the wallmarts,,I have found it has to do with the "complex" where they are located. Most,if not all wallmarts embrace you,but there seem to be some that are part of more a "private" shopping area.
      I'm in wv,and got chased out of a shopping mall area,by a wallmart in martinsburg wv. Otherwise,,30 minutes north,in Hagerstown Md. all was cool..
    • Frank
      I have been electrical contractor for about 30 years. Never have known of a gen set surge Please enlighten an old guy. Frank
      Message 2 of 13 , Nov 21, 2012
        I have been electrical contractor for about 30 years. Never have known of a gen set "surge" Please enlighten an old guy. Frank
      • Jerry Boone
        FRANK: I m not sure what the original writer has in mind, but on my 4K Onan, the generator will fire up and then spend minute after minute revving up and
        Message 3 of 13 , Nov 21, 2012
          FRANK:

          I'm not sure what the original writer has in mind, but on my 4K Onan, the generator will fire up and then spend minute after minute revving up and slowing down, revving up and slowing down. It will finally settle in to a decently smooth operation, right up until I put a heavy load on it. Runs fine with the microwave, does the surge routine when I turn on the AC.

          -- boone
          1989 Ultrastar 28'






          Once the game is over, the King and the pawn go back in the same box.
          - Italian Proverb





          -----Original Message-----
          From: Frank <frank.id.crown@...>
          To: classicrv <classicrv@yahoogroups.com>
          Sent: Wed, Nov 21, 2012 4:14 pm
          Subject: [classicrv] Please explain generator surge





          I have been electrical contractor for about 30 years. Never have known of a gen set "surge" Please enlighten an old guy. Frank









          [Non-text portions of this message have been removed]
        • rick haywood
          if yours is revving up and slowing down it needs to be adjusted properly and quite possibly need a carb cleaning and tune up, it should not surge at all when
          Message 4 of 13 , Nov 21, 2012
            if yours is revving up and slowing down it needs to be adjusted properly and quite possibly need a carb cleaning and tune up, it should not surge at all when started up. the act of revving up and down can make the voltage go down to a too low level and way to high which can burn up appliances. more often than not the cause is a varnished up carburetor. which means the fuel has set in the carburetor too long due to not running it often enough. onan recommends running it 2 to 3 hours a month, or using a fuel stabilizer in the fuel to keep the fuel fresh. one should also realize that a load is on it when you start in the form of the converter which can cost you alot of bucks if you burn it up.   rick


            ________________________________
            From: Jerry Boone <jfboone@...>
            To: classicrv@yahoogroups.com
            Sent: Wednesday, November 21, 2012 5:25 PM
            Subject: Re: [classicrv] Please explain generator surge


             
            FRANK:

            I'm not sure what the original writer has in mind, but on my 4K Onan, the generator will fire up and then spend minute after minute revving up and slowing down, revving up and slowing down. It will finally settle in to a decently smooth operation, right up until I put a heavy load on it. Runs fine with the microwave, does the surge routine when I turn on the AC.

            -- boone
            1989 Ultrastar 28'

            Once the game is over, the King and the pawn go back in the same box.
            - Italian Proverb

            -----Original Message-----
            From: Frank <frank.id.crown@...>
            To: classicrv <classicrv@yahoogroups.com>
            Sent: Wed, Nov 21, 2012 4:14 pm
            Subject: [classicrv] Please explain generator surge

            I have been electrical contractor for about 30 years. Never have known of a gen set "surge" Please enlighten an old guy. Frank

            [Non-text portions of this message have been removed]




            [Non-text portions of this message have been removed]
          • rick haywood
            onan s have been known to go below rated voltage of 120 sometimes down to 60volts and then rev up to over 150volts on a swing cycle. rick
            Message 5 of 13 , Nov 21, 2012
              onan's have been known to go below rated voltage of 120 sometimes down to 60volts and then rev up to over 150volts on a swing cycle. rick


              ________________________________
              From: Frank <frank.id.crown@...>
              To: classicrv@yahoogroups.com
              Sent: Wednesday, November 21, 2012 5:14 PM
              Subject: [classicrv] Please explain generator surge


               
              I have been electrical contractor for about 30 years. Never have known of a gen set "surge" Please enlighten an old guy. Frank




              [Non-text portions of this message have been removed]
            • Warren
              Gen set surge. Caused by a sudden change in load. And increase in load causes the gen to slow down due to load and then it throttles up to compensate and
              Message 6 of 13 , Nov 21, 2012
                Gen set surge. Caused by a sudden change in load. And increase in load causes the gen to slow down due to load and then it throttles up to compensate and over throttles a tad.
                The slow down causes the voltage to drop a bit and the over throttle causes it to go over voltage a little and thus....a gen set surge. A sudden drop in load can also cause the gen to over throttle a little. Air conditioners are bad about causing the gen to surge.


                --
                Warren
                1995 Ford F-350 Centurion 7.3 power stroke diesel dually (Sam).
                1953 Airstream Cruiser Travel trailer (The Runaway Sue)
                Western KY
                Sent from my iPad 2.

                On Nov 21, 2012, at 6:14 PM, "Frank" <frank.id.crown@...> wrote:

                > I have been electrical contractor for about 30 years. Never have known of a gen set "surge" Please enlighten an old guy. Frank
                >
                >


                [Non-text portions of this message have been removed]
              • Warren
                I would expect that from a cheap gen but not an Onan. Live and learn I guess. -- Warren 1995 Ford F-350 Centurion 7.3 power stroke diesel dually (Sam). 1953
                Message 7 of 13 , Nov 21, 2012
                  I would expect that from a cheap gen but not an Onan. Live and learn I guess.

                  --
                  Warren
                  1995 Ford F-350 Centurion 7.3 power stroke diesel dually (Sam).
                  1953 Airstream Cruiser Travel trailer (The Runaway Sue)
                  Western KY
                  Sent from my iPad 2.

                  On Nov 21, 2012, at 6:47 PM, rick haywood <haywood_rick@...> wrote:

                  > onan's have been known to go below rated voltage of 120 sometimes down to 60volts and then rev up to over 150volts on a swing cycle. rick
                  >
                  > ________________________________
                  > From: Frank <frank.id.crown@...>
                  > To: classicrv@yahoogroups.com
                  > Sent: Wednesday, November 21, 2012 5:14 PM
                  > Subject: [classicrv] Please explain generator surge
                  >
                  >
                  >
                  > I have been electrical contractor for about 30 years. Never have known of a gen set "surge" Please enlighten an old guy. Frank
                  >
                  > [Non-text portions of this message have been removed]
                  >
                  >


                  [Non-text portions of this message have been removed]
                • Ted Kroll
                  Frank, Does it have a load on it when it is surging? Ted ... From: Frank To: classicrv@yahoogroups.com Sent: Wednesday, November 21, 2012 6:14 PM Subject:
                  Message 8 of 13 , Nov 22, 2012
                    Frank, Does it have a load on it when it is surging?
                    Ted
                    ----- Original Message -----
                    From: Frank
                    To: classicrv@yahoogroups.com
                    Sent: Wednesday, November 21, 2012 6:14 PM
                    Subject: [classicrv] Please explain generator surge



                    I have been electrical contractor for about 30 years. Never have known of a gen set "surge" Please enlighten an old guy. Frank





                    [Non-text portions of this message have been removed]
                  • Jerry Boone
                    Again, I can t speak for Frank, but in my case it surges without a load, especially when it is first fired up. -- boone Once the game is over, the King and the
                    Message 9 of 13 , Nov 22, 2012
                      Again, I can't speak for Frank, but in my case it surges without a load, especially when it is first fired up.

                      -- boone






                      Once the game is over, the King and the pawn go back in the same box.
                      - Italian Proverb





                      -----Original Message-----
                      From: Ted Kroll <tedkroll@...>
                      To: classicrv <classicrv@yahoogroups.com>
                      Sent: Thu, Nov 22, 2012 6:36 am
                      Subject: Re: [classicrv] Please explain generator surge





                      Frank, Does it have a load on it when it is surging?
                      Ted
                      ----- Original Message -----
                      From: Frank
                      To: classicrv@yahoogroups.com
                      Sent: Wednesday, November 21, 2012 6:14 PM
                      Subject: [classicrv] Please explain generator surge

                      I have been electrical contractor for about 30 years. Never have known of a gen set "surge" Please enlighten an old guy. Frank

                      [Non-text portions of this message have been removed]









                      [Non-text portions of this message have been removed]
                    • Frank
                      My gen set does not surge. If a gen set is in good tune and set correctly there is just a very slight change in engine performance. The engines that surge
                      Message 10 of 13 , Nov 22, 2012
                        My gen set does not surge. If a gen set is in good tune and set correctly there is just a very slight change in engine performance. The engines that "surge" need some careful checking and setting of the engine. Engines that have rpm rise and fall are not set correctly as the fuel air/fuel adjustment. A bad air filter will also cause surge or hunting. Overall condition of the engine is important also. The surge is not a good thing. It is important for the engine to have the initial rpm set high enough to make the change to a higher rpm while under load. As I understand the process, the engine is set at a rpm until a load is placed upon the engine and the sail is moved and the throttle linkage is moved to more fuel. The throttle is at idle or advance under load. Checking the voltage is also important part of setting a gen set. I usually set the voltage at 125-130 vac. High voltage will not harm any equipment, but low voltage makes a rise in amperage. My view. Frank
                      • BMWslim@aol.com
                        I would set at 60 HZ and the voltage will be set. If you don t set HZ any motor that is used will be out of sink. RPM s should drop when demand is called for
                        Message 11 of 13 , Nov 22, 2012
                          I would set at 60 HZ and the voltage will be set. If you don't set HZ any
                          motor that is used will be out of sink.

                          RPM's should drop when demand is called for but governor should return it
                          to the original setting.




                          In a message dated 11/22/2012 11:02:26 A.M. Central Standard Time,
                          frank.id.crown@... writes:

                          My gen set does not surge. If a gen set is in good tune and set
                          correctly there is just a very slight change in engine performance. The engines
                          that "surge" need some careful checking and setting of the engine. Engines
                          that have rpm rise and fall are not set correctly as the fuel air/fuel
                          adjustment. A bad air filter will also cause surge or hunting. Overall
                          condition of the engine is important also. The surge is not a good thing. It is
                          important for the engine to have the initial rpm set high enough to make
                          the change to a higher rpm while under load. As I understand the process,
                          the engine is set at a rpm until a load is placed upon the engine and the
                          sail is moved and the throttle linkage is moved to more fuel. The throttle
                          is at idle or advance under load. Checking the voltage is also important
                          part of setting a gen set. I usually set the voltage at 125-130 vac. High
                          voltage will not harm any equipment, but low voltage makes a rise in
                          amperage. My view. F
                          rank



                          ------------------------------------

                          Yahoo! Groups Links






                          [Non-text portions of this message have been removed]
                        • Warren
                          Your gen manual says to let it run for about 5 minutes to warm up before running any electrical load on it. -- Warren 1995 Ford F-350 Centurion 7.3 power
                          Message 12 of 13 , Nov 22, 2012
                            Your gen manual says to let it run for about 5 minutes to warm up before running any electrical load on it.

                            --
                            Warren
                            1995 Ford F-350 Centurion 7.3 power stroke diesel dually (Sam).
                            1953 Airstream Cruiser Travel trailer (The Runaway Sue)
                            Western KY
                            Sent from my iPad 2.

                            On Nov 22, 2012, at 8:49 AM, Jerry Boone <jfboone@...> wrote:

                            > Again, I can't speak for Frank, but in my case it surges without a load, especially when it is first fired up.
                            >
                            > -- boone
                            >
                            > Once the game is over, the King and the pawn go back in the same box.
                            > - Italian Proverb
                            >
                            > -----Original Message-----
                            > From: Ted Kroll <tedkroll@...>
                            > To: classicrv <classicrv@yahoogroups.com>
                            > Sent: Thu, Nov 22, 2012 6:36 am
                            > Subject: Re: [classicrv] Please explain generator surge
                            >
                            > Frank, Does it have a load on it when it is surging?
                            > Ted
                            > ----- Original Message -----
                            > From: Frank
                            > To: classicrv@yahoogroups.com
                            > Sent: Wednesday, November 21, 2012 6:14 PM
                            > Subject: [classicrv] Please explain generator surge
                            >
                            > I have been electrical contractor for about 30 years. Never have known of a gen set "surge" Please enlighten an old guy. Frank
                            >
                            > [Non-text portions of this message have been removed]
                            >
                            > [Non-text portions of this message have been removed]
                            >
                            >


                            [Non-text portions of this message have been removed]
                          • Warren
                            And this drop and return will cause a surge. I will also, for those non inverter gen sets, change the Hz as well. -- Warren 1995 Ford F-350 Centurion 7.3
                            Message 13 of 13 , Nov 22, 2012
                              And this drop and return will cause a surge. I will also, for those non inverter gen sets, change the Hz as well.

                              --
                              Warren
                              1995 Ford F-350 Centurion 7.3 power stroke diesel dually (Sam).
                              1953 Airstream Cruiser Travel trailer (The Runaway Sue)
                              Western KY
                              Sent from my iPad 2.

                              On Nov 22, 2012, at 12:25 PM, BMWslim@... wrote:

                              > I would set at 60 HZ and the voltage will be set. If you don't set HZ any
                              > motor that is used will be out of sink.
                              >
                              > RPM's should drop when demand is called for but governor should return it
                              > to the original setting.
                              >
                              >
                              >
                              >
                              > In a message dated 11/22/2012 11:02:26 A.M. Central Standard Time,
                              > frank.id.crown@... writes:
                              >
                              > My gen set does not surge. If a gen set is in good tune and set
                              > correctly there is just a very slight change in engine performance. The engines
                              > that "surge" need some careful checking and setting of the engine. Engines
                              > that have rpm rise and fall are not set correctly as the fuel air/fuel
                              > adjustment. A bad air filter will also cause surge or hunting. Overall
                              > condition of the engine is important also. The surge is not a good thing. It is
                              > important for the engine to have the initial rpm set high enough to make
                              > the change to a higher rpm while under load. As I understand the process,
                              > the engine is set at a rpm until a load is placed upon the engine and the
                              > sail is moved and the throttle linkage is moved to more fuel. The throttle
                              > is at idle or advance under load. Checking the voltage is also important
                              > part of setting a gen set. I usually set the voltage at 125-130 vac. High
                              > voltage will not harm any equipment, but low voltage makes a rise in
                              > amperage. My view. F
                              > rank
                              >
                              > ------------------------------------
                              >
                              > Yahoo! Groups Links
                              >
                              > [Non-text portions of this message have been removed]
                              >
                              >


                              [Non-text portions of this message have been removed]