Add-135-2012ai-PPR4-Draft-11 issues

Expand Messages
  • goetz_philippe
    Hi, Here some comments regarding Add-135-2012ai-PPR4-Draft-11: Inconsistence between Table 23-1 and comment in Clause 21 for BACnetNetworkPortCommand Limits of
    Message 1 of 2 , Dec 11, 2013
    • 0 Attachment
      Hi,


      Here some comments regarding Add-135-2012ai-PPR4-Draft-11:

      Inconsistence between Table 23-1 and comment in Clause 21 for BACnetNetworkPortCommand
         Limits of reserved values 0..127 or 0..63!

      BACnetNetworkPortCommand in Clause 21
      ":: =" => "::=" remove space
      "discard- changes" => "discard-changes" - remove space
      '...' => "..." - character '...' to be replaced by three '.' (it exists other places where this also the case)

      BACnetPropertyIdentifier in Clause 21
      Duplicate (n+5) but (n+4) missing

      Regards,

      Philippe Goetz

       

      Siemens AG

      Infrastructure & Cities Sector

      Building Technologies Division

      IC BT SSP ES R&D DE MCH

      Siemensallee 84

      76187 Karlsruhe, Deutschland

      Tel: +49 721 595-8006

      Fax: +49  721  595-5112

       

      Siemens Aktiengesellschaft: Vorsitzender des Aufsichtsrats: Gerhard Cromme; Vorstand: Joe Kaeser, Vorsitzender; Roland Busch, Klaus Helmrich, Hermann Requardt, Siegfried Russwurm, Peter Y. Solmssen, Michael Süß, Ralf P. Thomas; Sitz der Gesellschaft: Berlin und München, Deutschland; Registergericht: Berlin Charlottenburg, HRB 12300, München, HRB 6684; WEEE-Reg.-Nr. DE 23691322

    • Coleman Brumley
      Phillipe, Thank you for pointing these out. I¹ve made these editorial changes to Add AI. Regards, Coleman ... Phillipe, Thank you for pointing these out. Ive
      Message 2 of 2 , Dec 11, 2013
      • 0 Attachment
        Phillipe,

        Thank you for pointing these out. I’ve made these editorial changes to Add AI. 

        Regards,
        Coleman

        On 12/11/13, 4:37 AM, "philippe.goetz@..." wrote:

         

        Hi,


        Here some comments regarding Add-135-2012ai-PPR4-Draft-11:

        Inconsistence between Table 23-1 and comment in Clause 21 for BACnetNetworkPortCommand
           Limits of reserved values 0..127 or 0..63!

        BACnetNetworkPortCommand in Clause 21
        ":: =" => "::=" remove space
        "discard- changes" => "discard-changes" - remove space
        '...' => "..." - character '...' to be replaced by three '.' (it exists other places where this also the case)

        BACnetPropertyIdentifier in Clause 21
        Duplicate (n+5) but (n+4) missing

        Regards,

        Philippe Goetz

         

        Siemens AG

        Infrastructure & Cities Sector

        Building Technologies Division

        IC BT SSP ES R&D DE MCH

        Siemensallee 84

        76187 Karlsruhe, Deutschland

        Tel: +49 721 595-8006

        Fax: +49  721  595-5112

         

        Siemens Aktiengesellschaft: Vorsitzender des Aufsichtsrats: Gerhard Cromme; Vorstand: Joe Kaeser, Vorsitzender; Roland Busch, Klaus Helmrich, Hermann Requardt, Siegfried Russwurm, Peter Y. Solmssen, Michael Süß, Ralf P. Thomas; Sitz der Gesellschaft: Berlin und München, Deutschland; Registergericht: Berlin Charlottenburg, HRB 12300, München, HRB 6684; WEEE-Reg.-Nr. DE 23691322

      Your message has been successfully submitted and would be delivered to recipients shortly.