    To; axialflux alt. member   From;  Jeff   Baldridge              I am glad I found somebody to communicate with. I am building an alternator
    Message 1 of 14 , Feb 13, 2012
    View Source
    • 0 Attachment
      To; axialflux alt. member
       
      From;  Jeff   Baldridge
       
                 I am glad I found somebody to communicate with. I am building an alternator from Hugh Piggots book. Mine has 9 coils and 12 magnets on each rotor. It is for a small hydroelectric turbine, so it will always turn at about the same RPM.
                  I want to put the electric output from the Alternator into the grid (grid-tie system) without using any batteries.I am wired into the rectifier now. that's is far as I have gotten now. I need a micro inverter with an input range of 10 to 30 volts. I need someone to show me how to wire this directly into my house electric  I need a diagram  and explanation and also where I can buy the micro inverter.  I could pay you a small fee for the information.                                     
    • drsimm@juno.com
      Jeff,This is NOT A TRIVIAL Task! If the phase and voltage level are not matched EXACTLY within less than 1 degree of the 60 cycles the grid has enough energy
      Message 2 of 14 , Feb 14, 2012
      View Source
      • 0 Attachment
        Jeff,
        This is NOT A TRIVIAL Task!
        If the phase and voltage level are not matched EXACTLY within less than 1 degree of the 60 cycles the "grid" has enough energy to rip your alternator physically off its concrete mounting blocks!  I have seen videos of 50 KW Generators weighing TONS haveing this done to them when not matched to the grid. 
        There is also a power factor to match as well. to get the energy "to the grid".
        You are MUCH BETTER getting a transfer switch inbetween the grid and your breaker box ,  
        cut off the grid and use your alternator on less circuits as the "least expensive option" .
         
        Look at grid tie inverters for wind power - good grid tie ones are ~= $5000.00 for a 4 -7KW one.
        DOn

        ---------- Original Message ----------
        From: jeff marcato <jbm775@...>
        To: "axialflux@yahoogroups.com" <axialflux@yahoogroups.com>
        Subject: [axialflux] Alternator
        Date: Mon, 13 Feb 2012 17:35:03 -0800 (PST)

         

        To; axialflux alt. member
         
        From;  Jeff   Baldridge
         
                   I am glad I found somebody to communicate with. I am building an alternator from Hugh Piggots book. Mine has 9 coils and 12 magnets on each rotor. It is for a small hydroelectric turbine, so it will always turn at about the same RPM.
                    I want to put the electric output from the Alternator into the grid (grid-tie system) without using any batteries.I am wired into the rectifier now. that's is far as I have gotten now. I need a micro inverter with an input range of 10 to 30 volts. I need someone to show me how to wire this directly into my house electric  I need a diagram  and explanation and also where I can buy the micro inverter.  I could pay you a small fee for the information.                                     

         

         



        ____________________________________________________________
        Groupon™ Official Site
        1 ridiculously huge coupon a day. Get 50-90% off your city's best!
        Groupon.com
      • Steve Spence
        The micro inverter he s talking about takes care of the phase and voltage issues. The only concern I have is not having the battery buffer . If the grid is
        Message 3 of 14 , Feb 14, 2012
        View Source
        • 0 Attachment
          The micro inverter he's talking about takes care of the phase and
          voltage issues. The only concern I have is not having the battery
          "buffer". If the grid is down, you are out of juice.


          --
          Steve Spence
          http://www.green-trust.org
          http://www.essnmag.com


          Quoting "drsimm@..." <drsimm@...>:

          > Jeff,This is NOT A TRIVIAL Task!
          > If the phase and voltage level are not matched EXACTLY within less
          > than 1 degree of the 60 cycles the "grid" has enough energy to rip
          > your alternator physically off its concrete mounting blocks! I have
          > seen videos of 50 KW Generators weighing TONS haveing this done to
          > them when not matched to the grid.
          > There is also a power factor to match as well. to get the energy "to
          > the grid".You are MUCH BETTER getting a transfer switch inbetween
          > the grid and your breaker box , cut off the grid and use your
          > alternator on less circuits as the "least expensive option" . Look
          > at grid tie inverters for wind power - good grid tie ones are ~=
          > $5000.00 for a 4 -7KW one.DOn
          >
          > ---------- Original Message ----------
          > From: jeff marcato <jbm775@...>
          > To: "axialflux@yahoogroups.com" <axialflux@yahoogroups.com>
          > Subject: [axialflux] Alternator
          > Date: Mon, 13 Feb 2012 17:35:03 -0800 (PST)
          >
          >
          >
          > To; axialflux alt. member From; Jeff Baldridge I am
          > glad I found somebody to communicate with. I am building an
          > alternator from Hugh Piggots book. Mine has 9 coils and 12 magnets
          > on each rotor. It is for a small hydroelectric turbine, so it will
          > always turn at about the same RPM. I want to put the
          > electric output from the Alternator into the grid (grid-tie system)
          > without using any batteries.I am wired into the rectifier now.
          > that's is far as I have gotten now. I need a micro inverter with an
          > input range of 10 to 30 volts. I need someone to show me how to wire
          > this directly into my house electric I need a diagram and
          > explanation and also where I can buy the micro inverter. I could
          > pay you a small fee for the information.
          >
          >
          > ____________________________________________________________
          > Groupon™ Official Site
          > 1 ridiculously huge coupon a day. Get 50-90% off your city's best!
          > http://thirdpartyoffers.juno.com/TGL3131/4f3a779ae660313ae388st05duc
        • drsimm@juno.com
          Micro inverter he is talking about ? Reference to same ? Is this a build yourself or a purchase product ? ... From: Steve Spence
          Message 4 of 14 , Feb 14, 2012
          View Source
          • 0 Attachment
            Micro inverter "he is talking about" ?
            Reference to same ? Is this a build yourself or a purchase product ?


            ---------- Original Message ----------
            From: Steve Spence <sspence@...>
            To: axialflux@yahoogroups.com
            Subject: Re: [axialflux] Alternator
            Date: Tue, 14 Feb 2012 09:21:40 -0600

             

            The micro inverter he's talking about takes care of the phase and
            voltage issues. The only concern I have is not having the battery
            "buffer". If the grid is down, you are out of juice.

            --
            Steve Spence
            http://www.green-trust.org
            http://www.essnmag.com

            Quoting "drsimm@..." <drsimm@...>:

            > Jeff,This is NOT A TRIVIAL Task!
            > If the phase and voltage level are not matched EXACTLY within less
            > than 1 degree of the 60 cycles the "grid" has enough energy to rip
            > your alternator physically off its concrete mounting blocks! I have
            > seen videos of 50 KW Generators weighing TONS haveing this done to
            > them when not matched to the grid.
            > There is also a power factor to match as well. to get the energy "to
            > the grid".You are MUCH BETTER getting a transfer switch inbetween
            > the grid and your breaker box , cut off the grid and use your
            > alternator on less circuits as the "least expensive option" . Look
            > at grid tie inverters for wind power - good grid tie ones are ~=
            > $5000.00 for a 4 -7KW one.DOn
            >
            > ---------- Original Message ----------
            > From: jeff marcato <jbm775@...>
            > To: "axialflux@yahoogroups.com" <axialflux@yahoogroups.com>
            > Subject: [axialflux] Alternator
            > Date: Mon, 13 Feb 2012 17:35:03 -0800 (PST)
            >
            >
            >
            > To; axialflux alt. member From; Jeff Baldridge I am
            > glad I found somebody to communicate with. I am building an
            > alternator from Hugh Piggots book. Mine has 9 coils and 12 magnets
            > on each rotor. It is for a small hydroelectric turbine, so it will
            > always turn at about the same RPM. I want to put the
            > electric output from the Alternator into the grid (grid-tie system)
            > without using any batteries.I am wired into the rectifier now.
            > that's is far as I have gotten now. I need a micro inverter with an
            > input range of 10 to 30 volts. I need someone to show me how to wire
            > this directly into my house electric I need a diagram and
            > explanation and also where I can buy the micro inverter. I could
            > pay you a small fee for the information.
            >
            >
            > __________________________________________________________
            > Groupon&#8482 Official Site
            > 1 ridiculously huge coupon a day. Get 50-90% off your city&#39;s best!
            > http://thirdpartyoffers.juno.com/TGL3131/4f3a779ae660313ae388st05duc

             

             



            ____________________________________________________________
            53 Year Old Mom Looks 33
            The Stunning Results of Her Wrinkle Trick Has Botox Doctors Worried
            consumerproducts.com
          • Steve Spence
            Look up enphase. -- Steve Spence http://www.green-trust.org http://www.essnmag.com
            Message 5 of 14 , Feb 14, 2012
            View Source
            • 0 Attachment
              Look up enphase.


              --
              Steve Spence
              http://www.green-trust.org
              http://www.essnmag.com


              Quoting "drsimm@..." <drsimm@...>:

              > Micro inverter "he is talking about" ?
              > Reference to same ? Is this a build yourself or a purchase product ?
              >
              > ---------- Original Message ----------
              > From: Steve Spence <sspence@...>
              > To: axialflux@yahoogroups.com
              > Subject: Re: [axialflux] Alternator
              > Date: Tue, 14 Feb 2012 09:21:40 -0600
              >
              >
              >
              > The micro inverter he's talking about takes care of the phase and
              > voltage issues. The only concern I have is not having the battery
              > "buffer". If the grid is down, you are out of juice.
              >
              > --
              > Steve Spence
              > http://www.green-trust.org
              > http://www.essnmag.com
              >
              > Quoting "drsimm@..." <drsimm@...>:
              >
              > > Jeff,This is NOT A TRIVIAL Task!
              > > If the phase and voltage level are not matched EXACTLY within less
              > > than 1 degree of the 60 cycles the "grid" has enough energy to rip
              > > your alternator physically off its concrete mounting blocks! I have
              > > seen videos of 50 KW Generators weighing TONS haveing this done to
              > > them when not matched to the grid.
              > > There is also a power factor to match as well. to get the energy "to
              > > the grid".You are MUCH BETTER getting a transfer switch inbetween
              > > the grid and your breaker box , cut off the grid and use your
              > > alternator on less circuits as the "least expensive option" . Look
              > > at grid tie inverters for wind power - good grid tie ones are ~=
              > > $5000.00 for a 4 -7KW one.DOn
              > >
              > > ---------- Original Message ----------
              > > From: jeff marcato <jbm775@...>
              > > To: "axialflux@yahoogroups.com" <axialflux@yahoogroups.com>
              > > Subject: [axialflux] Alternator
              > > Date: Mon, 13 Feb 2012 17:35:03 -0800 (PST)
              > >
              > >
              > >
              > > To; axialflux alt. member From; Jeff Baldridge I am
              > > glad I found somebody to communicate with. I am building an
              > > alternator from Hugh Piggots book. Mine has 9 coils and 12 magnets
              > > on each rotor. It is for a small hydroelectric turbine, so it will
              > > always turn at about the same RPM. I want to put the
              > > electric output from the Alternator into the grid (grid-tie system)
              > > without using any batteries.I am wired into the rectifier now.
              > > that's is far as I have gotten now. I need a micro inverter with an
              > > input range of 10 to 30 volts. I need someone to show me how to wire
              > > this directly into my house electric I need a diagram and
              > > explanation and also where I can buy the micro inverter. I could
              > > pay you a small fee for the information.
              > >
              > >
              > > __________________________________________________________
              > > Groupon™ Official Site
              > > 1 ridiculously huge coupon a day. Get 50-90% off your city's best!
              > > http://thirdpartyoffers.juno.com/TGL3131/4f3a779ae660313ae388st05duc
              >
              >
              >
              >
              >
            • larry@cargopal.com
              I am building a 4KW Volts A/C Grid-Tied Wind Turbine that uses a Micro Controller. What is your output Volts DC and amperage? I may be able to help. Larry in
              Message 6 of 14 , Feb 14, 2012
              View Source
              • 0 Attachment

                I am building a 4KW Volts A/C  Grid-Tied Wind Turbine that uses a Micro Controller. What is your output Volts DC and amperage? I may be able to help.

                Larry in TEXAS

                 

                From: axialflux@yahoogroups.com [mailto:axialflux@yahoogroups.com] On Behalf Of Steve Spence
                Sent: Tuesday, February 14, 2012 2:16 PM
                To: axialflux@yahoogroups.com
                Subject: Re: [axialflux] Alternator

                 

                 

                Look up enphase.

                --
                Steve Spence
                http://www.green-trust.org
                http://www.essnmag.com

                Quoting "drsimm@..." <drsimm@...>:

                > Micro inverter "he is talking about" ?
                > Reference to same ? Is this a build yourself or a purchase product ?
                >
                > ---------- Original Message ----------
                > From: Steve Spence <sspence@...>
                > To: axialflux@yahoogroups.com
                > Subject: Re: [axialflux] Alternator
                > Date: Tue, 14 Feb 2012 09:21:40 -0600
                >
                >
                >
                > The micro inverter he's talking about takes care of the phase and
                > voltage issues. The only concern I have is not having the battery
                > "buffer". If the grid is down, you are out of juice.
                >
                > --
                > Steve Spence
                > http://www.green-trust.org
                > http://www.essnmag.com
                >
                > Quoting "drsimm@..." <drsimm@...>:
                >
                > > Jeff,This is NOT A TRIVIAL Task!
                > > If the phase and voltage level are not matched EXACTLY within less
                > > than 1 degree of the 60 cycles the "grid" has enough energy to rip
                > > your alternator physically off its concrete mounting blocks! I have
                > > seen videos of 50 KW Generators weighing TONS haveing this done to
                > > them when not matched to the grid.
                > > There is also a power factor to match as well. to get the energy "to
                > > the grid".You are MUCH BETTER getting a transfer switch inbetween
                > > the grid and your breaker box , cut off the grid and use your
                > > alternator on less circuits as the "least expensive option" . Look
                > > at grid tie inverters for wind power - good grid tie ones are ~=
                > > $5000.00 for a 4 -7KW one.DOn
                > >
                > > ---------- Original Message ----------
                > > From: jeff marcato <jbm775@...>
                > > To: "axialflux@yahoogroups.com" <axialflux@yahoogroups.com>
                > > Subject: [axialflux] Alternator
                > > Date: Mon, 13 Feb 2012 17:35:03 -0800 (PST)
                > >
                > >
                > >
                > > To; axialflux alt. member From; Jeff Baldridge I am
                > > glad I found somebody to communicate with. I am building an
                > > alternator from Hugh Piggots book. Mine has 9 coils and 12 magnets
                > > on each rotor. It is for a small hydroelectric turbine, so it will
                > > always turn at about the same RPM. I want to put the
                > > electric output from the Alternator into the grid (grid-tie system)
                > > without using any batteries.I am wired into the rectifier now.
                > > that's is far as I have gotten now. I need a micro inverter with an
                > > input range of 10 to 30 volts. I need someone to show me how to wire
                > > this directly into my house electric I need a diagram and
                > > explanation and also where I can buy the micro inverter. I could
                > > pay you a small fee for the information.
                > >
                > >
                > > __________________________________________________________
                > > Groupon&#8482 Official Site
                > > 1 ridiculously huge coupon a day. Get 50-90% off your city&#39;s best!
                > > http://thirdpartyoffers.juno.com/TGL3131/4f3a779ae660313ae388st05duc
                >
                >
                >
                >
                >

              • jeff marcato
                Thank-you for your response Steve.I will be carefull. From: larry@cargopal.com To: axialflux@yahoogroups.com Sent: Tuesday, February 14,
                Message 7 of 14 , Feb 15, 2012
                View Source
                • 0 Attachment
                  Thank-you for your response Steve.I will be carefull.

                  From: "larry@..." <larry@...>
                  To: axialflux@yahoogroups.com
                  Sent: Tuesday, February 14, 2012 2:03 PM
                  Subject: [axialflux] Alternator micro controller

                  I am building a 4KW Volts A/C  Grid-Tied Wind Turbine that uses a Micro Controller. What is your output Volts DC and amperage? I may be able to help.
                  Larry in TEXAS
                   
                  From: axialflux@yahoogroups.com [mailto:axialflux@yahoogroups.com] On Behalf Of Steve Spence
                  Sent: Tuesday, February 14, 2012 2:16 PM
                  To: axialflux@yahoogroups.com
                  Subject: Re: [axialflux] Alternator
                   
                   
                  Look up enphase.

                  --
                  Steve Spence
                  http://www.green-trust.org
                  http://www.essnmag.com

                  Quoting "drsimm@..." <drsimm@...>:

                  > Micro inverter "he is talking about" ?
                  > Reference to same ? Is this a build yourself or a purchase product ?
                  >
                  > ---------- Original Message ----------
                  > From: Steve Spence <sspence@...>
                  > To: axialflux@yahoogroups.com
                  > Subject: Re: [axialflux] Alternator
                  > Date:
                  Tue, 14 Feb 2012 09:21:40 -0600
                  >
                  >
                  >
                  > The micro inverter he's talking about takes care of the phase and
                  > voltage issues. The only concern I have is not having the battery
                  > "buffer". If the grid is down, you are out of juice.
                  >
                  > --
                  > Steve Spence
                  > http://www.green-trust.org
                  > http://www.essnmag.com
                  >
                  > Quoting "drsimm@..." <drsimm@...>:
                  >
                  > > Jeff,This is NOT A TRIVIAL Task!
                  > > If the phase and voltage level are not matched EXACTLY within less
                  > > than 1 degree of the 60 cycles the "grid" has
                  enough energy to rip
                  > > your alternator physically off its concrete mounting blocks! I have
                  > > seen videos of 50 KW Generators weighing TONS haveing this done to
                  > > them when not matched to the grid.
                  > > There is also a power factor to match as well. to get the energy "to
                  > > the grid".You are MUCH BETTER getting a transfer switch inbetween
                  > > the grid and your breaker box , cut off the grid and use your
                  > > alternator on less circuits as the "least expensive option" . Look
                  > > at grid tie inverters for wind power - good grid tie ones are ~=
                  > > $5000.00 for a 4 -7KW one.DOn
                  > >
                  > > ---------- Original Message ----------
                  > > From: jeff marcato <jbm775@...>
                  > > To: "
                  target=_blank ymailto="mailto:axialflux%40yahoogroups.com">axialflux@yahoogroups.com" <axialflux@yahoogroups.com>
                  > > Subject: [axialflux] Alternator
                  > > Date: Mon, 13 Feb 2012 17:35:03 -0800 (PST)
                  > >
                  > >
                  > >
                  > > To; axialflux alt. member From; Jeff Baldridge I am
                  > > glad I found somebody to communicate with. I am building an
                  > > alternator from Hugh Piggots book. Mine has 9 coils and 12 magnets
                  > > on each rotor. It is for a small hydroelectric turbine, so it will
                  > > always turn at about the same RPM. I want to put the
                  > > electric output from the Alternator into the grid (grid-tie system)
                  > > without using any batteries.I am wired into the rectifier now.
                  > > that's is far as I have gotten now. I need a
                  micro inverter with an
                  > > input range of 10 to 30 volts. I need someone to show me how to wire
                  > > this directly into my house electric I need a diagram and
                  > > explanation and also where I can buy the micro inverter. I could
                  > > pay you a small fee for the information.
                  > >
                  > >
                  > > __________________________________________________________
                  > > Groupon&#8482 Official Site
                  > > 1 ridiculously huge coupon a day. Get 50-90% off your city&#39;s best!
                  > > http://thirdpartyoffers.juno.com/TGL3131/4f3a779ae660313ae388st05duc
                  >
                  >
                  >
                  >
                  >


                • jeff marcato
                  Larry;   I will check the dc output and get back to you .  Thanks From: larry@cargopal.com To: axialflux@yahoogroups.com Sent:
                  Message 8 of 14 , Feb 15, 2012
                  View Source
                  • 0 Attachment
                    Larry;   I will check the dc output and get back to you .  Thanks

                    From: "larry@..." <larry@...>
                    To: axialflux@yahoogroups.com
                    Sent: Tuesday, February 14, 2012 2:03 PM
                    Subject: [axialflux] Alternator micro controller

                    I am building a 4KW Volts A/C  Grid-Tied Wind Turbine that uses a Micro Controller. What is your output Volts DC and amperage? I may be able to help.
                    Larry in TEXAS
                     
                    From: axialflux@yahoogroups.com [mailto:axialflux@yahoogroups.com] On Behalf Of Steve Spence
                    Sent: Tuesday, February 14, 2012 2:16 PM
                    To: axialflux@yahoogroups.com
                    Subject: Re: [axialflux] Alternator
                     
                     
                    Look up enphase.

                    --
                    Steve Spence
                    http://www.green-trust.org
                    http://www.essnmag.com

                    Quoting "drsimm@..." <drsimm@...>:

                    > Micro inverter "he is talking about" ?
                    > Reference to same ? Is this a build yourself or a purchase product ?
                    >
                    > ---------- Original Message ----------
                    > From: Steve Spence <sspence@...>
                    > To: axialflux@yahoogroups.com
                    > Subject: Re: [axialflux] Alternator
                    > Date:
                    Tue, 14 Feb 2012 09:21:40 -0600
                    >
                    >
                    >
                    > The micro inverter he's talking about takes care of the phase and
                    > voltage issues. The only concern I have is not having the battery
                    > "buffer". If the grid is down, you are out of juice.
                    >
                    > --
                    > Steve Spence
                    > http://www.green-trust.org
                    > http://www.essnmag.com
                    >
                    > Quoting "drsimm@..." <drsimm@...>:
                    >
                    > > Jeff,This is NOT A TRIVIAL Task!
                    > > If the phase and voltage level are not matched EXACTLY within less
                    > > than 1 degree of the 60 cycles the "grid" has
                    enough energy to rip
                    > > your alternator physically off its concrete mounting blocks! I have
                    > > seen videos of 50 KW Generators weighing TONS haveing this done to
                    > > them when not matched to the grid.
                    > > There is also a power factor to match as well. to get the energy "to
                    > > the grid".You are MUCH BETTER getting a transfer switch inbetween
                    > > the grid and your breaker box , cut off the grid and use your
                    > > alternator on less circuits as the "least expensive option" . Look
                    > > at grid tie inverters for wind power - good grid tie ones are ~=
                    > > $5000.00 for a 4 -7KW one.DOn
                    > >
                    > > ---------- Original Message ----------
                    > > From: jeff marcato <jbm775@...>
                    > > To: "
                    target=_blank ymailto="mailto:axialflux%40yahoogroups.com">axialflux@yahoogroups.com" <axialflux@yahoogroups.com>
                    > > Subject: [axialflux] Alternator
                    > > Date: Mon, 13 Feb 2012 17:35:03 -0800 (PST)
                    > >
                    > >
                    > >
                    > > To; axialflux alt. member From; Jeff Baldridge I am
                    > > glad I found somebody to communicate with. I am building an
                    > > alternator from Hugh Piggots book. Mine has 9 coils and 12 magnets
                    > > on each rotor. It is for a small hydroelectric turbine, so it will
                    > > always turn at about the same RPM. I want to put the
                    > > electric output from the Alternator into the grid (grid-tie system)
                    > > without using any batteries.I am wired into the rectifier now.
                    > > that's is far as I have gotten now. I need a
                    micro inverter with an
                    > > input range of 10 to 30 volts. I need someone to show me how to wire
                    > > this directly into my house electric I need a diagram and
                    > > explanation and also where I can buy the micro inverter. I could
                    > > pay you a small fee for the information.
                    > >
                    > >
                    > > __________________________________________________________
                    > > Groupon&#8482 Official Site
                    > > 1 ridiculously huge coupon a day. Get 50-90% off your city&#39;s best!
                    > > http://thirdpartyoffers.juno.com/TGL3131/4f3a779ae660313ae388st05duc
                    >
                    >
                    >
                    >
                    >


                  • jerry freedomev
                                           Hi Jeff and All,                                           Or better Jeff
                    Message 9 of 14 , Feb 15, 2012
                    View Source
                    • 0 Attachment
                       
                                           Hi Jeff and All,
                       
                                                              Or better Jeff is make the voltage/cycle/phase match and drive the  grid directly. Far less costly, more reliable, etc.  A soft start is easy to do, just use resistors starting then when sync'ed, short out the restistors amoong other methods.
                                                              If 3ph grid you just need to match the coils turn numbers to get the voltage.  If 1 phase then you'd need to wind a single phase set up.
                                                              The big advantage of hydro is direct alt to grid without batts or inverters.
                       
                                                                                                        Jerry Dycus
                       
                       
                       
                      > > ---------- Original Message ----------
                      > > From: jeff marcato <jbm775@...>
                      > > To: "axialflux@yahoogroups.com" <axialflux@yahoogroups.com>
                      > > Subject: [axialflux] Alternator
                      > > Date: Mon, 13 Feb 2012 17:35:03 -0800 (PST)
                      > >
                      > >
                      > >
                      > > To; axialflux alt. member From; Jeff Baldridge I am
                      > > glad I found somebody to communicate with. I am building an
                      > > alternator from Hugh Piggots book. Mine has 9 coils and 12 magnets
                      > > on each
                      rotor. It is for a small hydroelectric turbine, so it will
                      > > always turn at about the same RPM. I want to put the
                      > > electric output from the Alternator into the grid (grid-tie system)
                      > > without using any batteries.I am wired into the rectifier now.
                      > > that's is far as I have gotten now. I need a micro inverter with an
                      > > input range of 10 to 30 volts. I need someone to show me how to wire
                      > > this directly into my house electric I need a diagram and
                      > > explanation and also where I can buy the micro inverter. I could
                      > > pay you a small fee for the information.
                      > >
                      > >
                      > > __________________________________________________________
                      > > Groupon&#8482 Official Site
                      > > 1 ridiculously huge coupon a day. Get 50-90% off your city&#39;s best!
                      > >
                      http://thirdpartyoffers.juno.com/TGL3131/4f3a779ae660313ae388st05duc
                      >
                      >
                      >
                      >
                      >






                    • Steve Spence
                      The hugh piggott style alternator is not designed for direct grid attachment. There is no way to synchronize the rpm. It s wild three phase and requires
                      Message 10 of 14 , Feb 15, 2012
                      View Source
                      • 0 Attachment
                        The hugh piggott style alternator is not designed for direct grid
                        attachment. There is no way to synchronize the rpm. It's wild three
                        phase and requires rectification to dc, preferably for battery
                        storage, and use a grid tie inverter if you must connect to the grid.


                        --
                        Steve Spence
                        http://www.green-trust.org
                        http://www.essnmag.com


                        Quoting jerry freedomev <freedomev@...>:

                        >  
                        >                      Hi Jeff and
                        > All,
                        >  
                        >                                         Or better Jeff is make the voltage/cycle/phase match and drive the  grid directly. Far less costly, more reliable, etc.  A soft start is easy to do, just use resistors starting then when sync'ed, short out the restistors amoong other
                        > methods.
                        >                                         If 3ph grid you just need to match the coils turn numbers to get the voltage.  If 1 phase then you'd need to wind a single phase set
                        > up.
                        >                                         The big advantage of hydro is direct alt to grid without batts or
                        > inverters.
                        >  
                        >                                                                                   Jerry
                        > Dycus
                        >  
                        >  
                        >  
                        >> > ---------- Original Message ----------
                        >> > From: jeff marcato <jbm775@...>
                        >> > To: "axialflux@yahoogroups.com" <axialflux@yahoogroups.com>
                        >> > Subject: [axialflux] Alternator
                        >> > Date: Mon, 13 Feb 2012 17:35:03 -0800 (PST)
                        >> >
                        >> >
                        >> >
                        >> > To; axialflux alt. member From; Jeff Baldridge I am
                        >> > glad I found somebody to communicate with. I am building an
                        >> > alternator from Hugh Piggots book. Mine has 9 coils and 12 magnets
                        >> > on each rotor. It is for a small hydroelectric turbine, so it will
                        >> > always turn at about the same RPM. I want to put the
                        >> > electric output from the Alternator into the grid (grid-tie system)
                        >> > without using any batteries.I am wired into the rectifier now.
                        >> > that's is far as I have gotten now. I need a micro inverter with an
                        >> > input range of 10 to 30 volts. I need someone to show me how to wire
                        >> > this directly into my house electric I need a diagram and
                        >> > explanation and also where I can buy the micro inverter. I could
                        >> > pay you a small fee for the information.
                        >> >
                        >> >
                        >> > __________________________________________________________
                        >> > Groupon™ Official Site
                        >> > 1 ridiculously huge coupon a day. Get 50-90% off your city's best!
                        >> > http://thirdpartyoffers.juno.com/TGL3131/4f3a779ae660313ae388st05duc
                        >>
                        >>
                        >>
                        >>
                        >>
                        >
                        >
                        >
                        >
                        >
                        >
                      • jerry freedomev
                                                    Hi Steve and All,                          
                        Message 11 of 14 , Feb 15, 2012
                        View Source
                        • 0 Attachment
                           
                                                    Hi Steve and All,
                                                   
                                                                While that is true with variable speed units but he was talking fixed rpm hydro which is completely different.   You'd need a 3ph grid to connect the standard 12 magnet/9 coil or change to even number of coils. mags and make a single phase stator. RPM depends of course on poles.  No different than other single/3ph alts on the grid.
                                                               How do you think other 1-3ph syncronous motors, alts run on the grid? There are many ways to match them up like I said, just google electric motor starting circuits. Most don't require anything except switching on like you do many times/day.   If you are playing with 50kw then there could be problems but 1-2kw just isn't a big deal.
                           
                                                                                                  Jerry Dycus
                           
                                                                
                          From: Steve Spence <sspence@...>
                          To: axialflux@yahoogroups.com
                          Sent: Wednesday, February 15, 2012 8:34 PM
                          Subject: Re: [axialflux] direct grid tie, Alternator micro controller

                          The hugh piggott style alternator is not designed for direct grid 
                          attachment. There is no way to synchronize the rpm. It's wild three 
                          phase and requires rectification to dc, preferably for battery 
                          storage, and use a grid tie inverter if you must connect to the grid.


                          --
                          Steve Spence
                          http://www.green-trust.org
                          http://www.essnmag.com

                        • thorthesailor
                          Could a bank of ultracapacitors stand in for batteries to provide some smoothing, allowing an all-off-the-shelf-components system? (Without the downsides of
                          Message 12 of 14 , May 1, 2012
                          View Source
                          • 0 Attachment
                            Could a bank of ultracapacitors stand in for batteries to provide some smoothing, allowing an all-off-the-shelf-components system?

                            (Without the downsides of batteries)

                            Michael


                            --- In axialflux@yahoogroups.com, jeff marcato <jbm775@...> wrote:
                            >
                            > To; axialflux alt. member
                            >  
                            > From;  Jeff   Baldridge
                            >  
                            >            I am glad I found somebody to communicate with. I am building an alternator from Hugh Piggots book. Mine has 9 coils and 12 magnets on each rotor. It is for a small hydroelectric turbine, so it will always turn at about the same RPM.
                            >             I want to put the electric output from the Alternator into the grid (grid-tie system) without using any batteries.I am wired into the rectifier now. that's is far as I have gotten now. I need a micro inverter with an input range of 10 to 30 volts. I need someone to show me how to wire this directly into my house electric  I need a diagram  and explanation and also where I can buy the micro inverter.  I could pay you a small fee for the information.                                     
                            >
                          • Steve Spence
                            The capacitors would cost more than the batteries. -- Steve Spence KK4HFJ http://www.green-trust.org http://www.essnmag.com
                            Message 13 of 14 , May 1, 2012
                            View Source
                            • 0 Attachment
                              The capacitors would cost more than the batteries.

                              --
                              Steve Spence KK4HFJ
                              http://www.green-trust.org
                              http://www.essnmag.com


                              Quoting thorthesailor <sailorthor@...>:

                              > Could a bank of ultracapacitors stand in for batteries to provide
                              > some smoothing, allowing an all-off-the-shelf-components system?
                              >
                              > (Without the downsides of batteries)
                              >
                              > Michael
                              >
                              >
                              > --- In axialflux@yahoogroups.com, jeff marcato <jbm775@...> wrote:
                              >>
                              >> To; axialflux alt. member
                              >>  
                              >> From;  Jeff   Baldridge
                              >>  
                              >>            I am
                              >> glad I found somebody to communicate with. I am building an
                              >> alternator from Hugh Piggots book. Mine has 9 coils and 12 magnets
                              >> on each rotor. It is for a small hydroelectric turbine, so it will
                              >> always turn at about the same RPM.
                              >>            
                              >> I want to put the electric output from the Alternator into the grid
                              >> (grid-tie system) without using any batteries.I am wired into the
                              >> rectifier now. that's is far as I have gotten now. I need a micro
                              >> inverter with an input range of 10 to 30 volts. I need someone to
                              >> show me how to wire this directly into my house electric 
                              >> I need a diagram  and explanation and also where I can buy the
                              >> micro inverter.  I could pay you a small fee for the
                              >> information.                                     
                              >>
                              >
                              >
                              >
                            • Michael
                              The ultracapacitors, if you caculate their life cycles, only last a couple years. http://www.cde.com/catalog/inverter/ If you over spec the voltage, (use a
                              Message 14 of 14 , May 2, 2012
                              View Source
                              • 0 Attachment
                                The ultracapacitors, if you caculate their life cycles, only last a couple years.
                                http://www.cde.com/catalog/inverter/

                                If you over spec the voltage, (use a 200V cap on a 100V peak ssytem) you may improve the lifetime.

                                You also may need to "fuse" the cap bank, and the additional impedence of the fuse, may decouple the bank.

                                Try the applets at the above link

                                --- In axialflux@yahoogroups.com, "thorthesailor" <sailorthor@...> wrote:
                                >
                                > Could a bank of ultracapacitors stand in for batteries to provide some smoothing, allowing an all-off-the-shelf-components system?
                                >
                                > (Without the downsides of batteries)
                                >
                                > Michael
                                >
                                >
                                > --- In axialflux@yahoogroups.com, jeff marcato <jbm775@> wrote:
                                > >
                                > > To; axialflux alt. member
                                > >  
                                > > From;  Jeff   Baldridge
                                > >  
                                > >            I am glad I found somebody to communicate with. I am building an alternator from Hugh Piggots book. Mine has 9 coils and 12 magnets on each rotor. It is for a small hydroelectric turbine, so it will always turn at about the same RPM.
                                > >             I want to put the electric output from the Alternator into the grid (grid-tie system) without using any batteries.I am wired into the rectifier now. that's is far as I have gotten now. I need a micro inverter with an input range of 10 to 30 volts. I need someone to show me how to wire this directly into my house electric  I need a diagram  and explanation and also where I can buy the micro inverter.  I could pay you a small fee for the information.                                     
                                > >
                                >
                              Your message has been successfully submitted and would be delivered to recipients shortly.