Re: [axialflux] 4.5 ACvolts/phase, but slows down when i connect it to rectifier

Expand Messages
  • Steve Spence
    Battery charging time is determined by how many ah s were removed from the battery, and how many amps your charger puts out. If you removed 75 ah s from the
    Message 1 of 26 , May 1, 2010
    View Source
    • 0 Attachment
      Battery charging time is determined by how many ah's were removed from
      the battery, and how many amps your charger puts out. If you removed 75
      ah's from the battery, and your charger produces 25 amps, then it will
      take theoretically 3 hours to recharge. Actually it will take longer as
      charging slows as the battery fills, and it takes about 20% more ah's to
      fill than you took out due to chemistry inefficiency.

      put an amp meter (or better yet an AH meter) on your circuit so you can
      see what's happening.

      Steve Spence
      Renewable energy and self sufficiency
      http://www.green-trust.org
      http://makingthewebwork.blogspot.com/



      On 04/30/2010 06:06 AM, sanjeev rao wrote:
      >
      >
      > Good day members
      >
      > I have connected Generator and at 200 RPM it produces 24+ ACvolts/phase,
      > but when i tried connecting rectifiers it was showing me only 18+DCV, i
      > was in a impression that 24 ACV x 1.73 = DCvoltage output, but it has
      > turned up otherway
      >
      > so i tried charging my battery (10Ah 12V battery) it took almost 6 hours
      > to charge complete battery from 4.7V to 12.6 V
      >
      > then i was suspecting the battery , tried charging bike battery 2.5Ah
      > L-C , even that took close to 1 hours.
      >
      > what am i doing mistake, is the output not sufficient? not much of amps,
      >
      > configuration of stator has got changed to 250Turns #18 wires per coil
      > so per phase 500 turns of #18 wire and two coils per phase. Over all 6
      > coils providing 3 phase,
      >
      > with the help of multimeter, when i checked the Ohms it was showing
      > 2ohms for two coils connected together
      >
      > Also i noticed when i connected to 2.5 Ah battery the rotation has got
      > reduced to 70+RPM not the 200RPM
      >
      > what went wrong
      >
      >
      > --- On *Tue, 4/27/10, sanjeev rao /<sosweet_san@...>/* wrote:
      >
      >
      > From: sanjeev rao <sosweet_san@...>
      > Subject: Re: [axialflux] 4.5 ACvolts/phase, but slows down when i
      > connect it to rectifier
      > To: axialflux@yahoogroups.com
      > Date: Tuesday, April 27, 2010, 7:44 AM
      >
      > thats great info steve, honestly i am getting boosted by these
      > answers, surely this week i will achieve this goal and get back to you.
      >
      > because of you and fellow members like charles, i could reach, from
      > 4.5V to 24V
      >
      > thanks steve spence, charles evans
      >
      > -sanjeev
      >
      >
      > --- On *Tue, 4/27/10, Steve Spence /<sspence@...>/* wrote:
      >
      >
      > From: Steve Spence <sspence@...>
      > Subject: Re: [axialflux] 4.5 ACvolts/phase, but slows down when
      > i connect it to rectifier
      > To: axialflux@yahoogroups.com
      > Date: Tuesday, April 27, 2010, 1:11 AM
      >
      >
      >
      > I would not suggest wiring for 240. I would suggest wiring for
      > 24 or 48
      > volts, and use an inverter to get your 240vac. Then you don't
      > have to
      > worry about frequency (rpm) regulation.
      >
      > The tail of the turbine will keep voltages down, and a dump
      > controller
      > will prevent over charging.
      >
      > Steve Spence
      > Renewable energy and self sufficiency
      > http://www.green- trust.org <http://www.green-trust.org>
      > http://makingtheweb work.blogspot. com/
      > <http://makingthewebwork.blogspot.com/>
      >
      > sanjeev rao wrote:
      > >
      > >
      > > its very clear now steve,
      > >
      > > if i have to get 240 volts output, either i need to have
      > 360*10 turns or
      > > 20 coils per phase,
      > >
      > > now these coils are weighing 500grams per coil i.e 1kg per phase
      > >
      > > does this weight also make difference?
      > >
      > > also if we produce more voltage is it possible we can regulate
      > it to
      > > 12DCV or 24DCV from 36Vdcv or some high odd voltages?
      > >
      > >
      > >
      > > --- On *Sat, 4/24/10, Steve Spence /<sspence@green-
      > trust.org>/* wrote:
      > >
      > >
      > > From: Steve Spence <sspence@green- trust.org>
      > > Subject: Re: [axialflux] 4.5 ACvolts/phase, but slows down when i
      > > connect it to rectifier
      > > To: axialflux@yahoogrou ps.com
      > > Date: Saturday, April 24, 2010, 6:31 PM
      > >
      > >
      > >
      > > 24v / phase is still 24v output. the phase voltages do not add.
      > >
      > > If using 2 coils per phase, You will need to wind 120v coils.
      > if you are
      > > using 3 coils per phase, then wind 80v coils.
      > >
      > > Steve Spence
      > > Renewable energy and self sufficiency
      > > http://www.green- trust.org <http://www.green- trust.org
      > <http://www.green-trust.org>>
      > > http://makingtheweb work.blogspot. com/
      > > <http://makingtheweb work.blogspot. com/
      > <http://makingthewebwork.blogspot.com/>>
      > >
      > > sanjeev rao wrote:
      > > >
      > > >
      > > > thanks steve, as per your guidance, the device is making
      > good result,
      > > >
      > > >
      > > > now it produces 12ACV/coil , six coils in 3phases, (2per phase
      > > 180turns
      > > > of #17 / coil and per phase 360 turns,), if we have to get 240
      > > volt ac,
      > > > what would be the best approach here we need to?
      > > >
      > > > is this calculations right?
      > > >
      > > > 12 x 2 = 24ACV per phase and 72ACV
      > > >
      > > > or if we can use any other wire size like #19awg or #20awg
      > will that
      > > > make difference?
      > > >
      > > > --
      > > >
      > > >
      > > > --- On *Thu, 4/22/10, Steve Spence /<sspence@green- trust.org
      > > </mc/compose? to=sspence% 40green-trust. org>>/* wrote:
      > > >
      > > >
      > > > From: Steve Spence <sspence@green- trust.org
      > > </mc/compose? to=sspence% 40green-trust. org>>
      > > > Subject: Re: [axialflux] 4.5 ACvolts/phase, but slows down
      > when i
      > > > connect it to rectifier
      > > > To: axialflux@yahoogrou ps.com
      > > </mc/compose? to=axialflux% 40yahoogroups. com>
      > > > Date: Thursday, April 22, 2010, 4:03 PM
      > > >
      > > >
      > > >
      > > > If whatever is turning the alt (hydro, engine, whatever) has rpm
      > > > control, ie. a governor, then you will get constant output.
      > > >
      > > > Steve Spence
      > > > Renewable energy and self sufficiency
      > > > http://www.green- trust.org <http://www.green- trust.org
      > > <http://www.green- trust.org <http://www.green-trust.org>>>
      > > > http://makingtheweb work.blogspot. com/
      > > > <http://makingtheweb work.blogspot. com/
      > > <http://makingtheweb work.blogspot. com/
      > <http://makingthewebwork.blogspot.com/>>>
      > > >
      > > > sanjeev rao wrote:
      > > > >
      > > > >
      > > > > Hi again
      > > > >
      > > > > might be a stupid query, dont know how to format this query,
      > > > >
      > > > > what do i need to do if i have to get constant output from
      > this
      > > device
      > > > >
      > > > > one thing is if it is constant RPM, then it can produce
      > constant
      > > > output,
      > > > > in that case can i avoid battery banking,
      > > > >
      > > > > like a petrol generator?
      > > > >
      > > > > --sanjeev
      > > > >
      > > > > --- On *Mon, 4/19/10, sanjeev rao /<sosweet_san@ yahoo.com
      > > > </mc/compose? to=sosweet_ san%40yahoo. com>>/* wrote:
      > > > >
      > > > >
      > > > > From: sanjeev rao <sosweet_san@ yahoo.com
      > > > </mc/compose? to=sosweet_ san%40yahoo. com>>
      > > > > Subject: Re: [axialflux] 4.5 ACvolts/phase, but slows down
      > when i
      > > > > connect it to rectifier
      > > > > To: axialflux@yahoogrou ps.com
      > > > </mc/compose? to=axialflux% 40yahoogroups. com>
      > > > > Date: Monday, April 19, 2010, 6:34 AM
      > > > >
      > > > >
      > > > >
      > > > > thanks steve and Charles Evans,
      > > > >
      > > > > i am trying to achieve 700+watts at this rpm,
      > > > >
      > > > > let me start winding a new stator
      > > > >
      > > > > --- On *Mon, 4/19/10, Steve Spence /<sspence@green-
      > trust.org>/*
      > > > wrote:
      > > > >
      > > > >
      > > > > From: Steve Spence <sspence@green- trust.org>
      > > > > Subject: Re: [axialflux] 4.5 ACvolts/phase, but slows down
      > when
      > > > > i connect it to rectifier
      > > > > To: axialflux@yahoogrou ps.com
      > > > > Date: Monday, April 19, 2010, 1:43 AM
      > > > >
      > > > >
      > > > >
      > > > > I use 70 turns of 14g.
      > > > >
      > > > > Steve Spence
      > > > > Renewable energy and self sufficiency
      > > > > http://www.green- trust.org <http://www.green- trust.org
      > > > <http://www.green- trust.org <http://www.green- trust.org
      > <http://www.green-trust.org>>>>
      > > > > http://makingtheweb work.blogspot. com/
      > > > > <http://makingtheweb work.blogspot. com/
      > > > <http://makingtheweb work.blogspot. com/
      > > <http://makingtheweb work.blogspot. com/
      > <http://makingthewebwork.blogspot.com/>>>>
      > > > >
      > > > > sanjeev rao wrote:
      > > > > >
      > > > > >
      > > > > > thanks steve
      > > > > >
      > > > > > i tried with my car alternator rectifier(Denso alternator
      > > > > 12V), it shows
      > > > > > me 7.1V at DCV
      > > > > >
      > > > > > If i have to rewind the entire set of coils, and this time i
      > > > > would like
      > > > > > to go for 9 coils 12 magnets in 10" disc, for 24V how many
      > > > > turns i need
      > > > > > to wind? is there any formulae or any simple method to
      > arrive
      > > > > this turn
      > > > > > calculations?
      > > > > >
      > > > > > please help!
      > > > > >
      > > > > > --sanjeev
      > > > > >
      > > > > > --- On *Wed, 4/14/10, Steve Spence /<sspence@green-
      > > > > trust.org>/* wrote:
      > > > > >
      > > > > >
      > > > > > From: Steve Spence <sspence@green- trust.org>
      > > > > > Subject: Re: [axialflux] 4.5 ACvolts/phase, but slows
      > down when i
      > > > > > connect it to rectifier
      > > > > > To: axialflux@yahoogrou ps.com
      > > > > > Date: Wednesday, April 14, 2010, 3:48 PM
      > > > > >
      > > > > >
      > > > > >
      > > > > > I use 100 amp 600v diodes in my 3 phase rectifiers. I
      > also use
      > > > > double
      > > > > > strands of 14g for 12v units, and single strand 14g for
      > 24v units.
      > > > > >
      > > > > > Voltage is subject to the number of turns, and size of the
      > > > > coil (and
      > > > > > strength of magnet and rpm), but the inventor of this
      > > > > technology, Hugh
      > > > > > Piggott, made this determination. Doubling the number of
      > > > > turns, doubles
      > > > > > the voltage.
      > > > > >
      > > > > > Steve Spence
      > > > > > Renewable energy and self sufficiency
      > > > > > http://www.green- trust.org <http://www.green- trust.org
      > > > > <http://www.green- trust.org <http://www.green- trust.org
      > > <http://www.green- trust.org <http://www.green-trust.org>>>>>
      > > > > > http://makingtheweb work.blogspot. com/
      > > > > > <http://makingtheweb work.blogspot. com/
      > > > > <http://makingtheweb work.blogspot. com/
      > > > <http://makingtheweb work.blogspot. com/
      > > <http://makingtheweb work.blogspot. com/
      > <http://makingthewebwork.blogspot.com/>>>>>
      > > > > >
      > > > > > sanjeev rao wrote:
      > > > > > >
      > > > > > >
      > > > > > > yes this is how it is connected
      > > > > > >
      > > > > > > coils 1 & 4 in series, 2 & 5 in series, and 3 & 6
      > > > > > > in series,
      > > > > > >
      > > > > > >
      > > > > > >>>but you would need 6 diodes, not 4, per my diagram
      > > > > > >
      > > > > > > what type of diode's i need to buy?
      > > > > > >
      > > > > > > also how do you arrive 105 turns per phase will
      > produce 12v? (my
      > > > > > > apologies, is this 17g wire or 14g?)
      > > > > > > if i use 210turns will it produces 24 volts, for 48 v?
      > > > > > >
      > > > > > >
      > > > > > >
      > > > > > > --- On *Wed, 4/14/10, Steve Spence /<sspence@green-
      > trust.org
      > > > > > </mc/compose? to=sspence% 40green-trust. org>>/* wrote:
      > > > > > >
      > > > > > >
      > > > > > > From: Steve Spence <sspence@green- trust.org
      > > > > > </mc/compose? to=sspence% 40green-trust. org>>
      > > > > > > Subject: Re: [axialflux] 4.5 ACvolts/phase, but slows down
      > > > > when i
      > > > > > > connect it to rectifier
      > > > > > > To: axialflux@yahoogrou ps.com
      > > > > > </mc/compose? to=axialflux% 40yahoogroups. com>
      > > > > > > Date: Wednesday, April 14, 2010, 4:00 AM
      > > > > > >
      > > > > > >
      > > > > > >
      > > > > > > a two phase unit would have coils 1 & 3 in series, and
      > 2 & 4 in
      > > > > > series.
      > > > > > > You can't do a 2 phase with 6 coils, but only 2 in
      > series. you
      > > > > > could do
      > > > > > > a 3 phase unit, with coils 1 & 4 in series, 2 & 5 in
      > series,
      > > > > and 3 & 6
      > > > > > > in series, but you would need 6 diodes, not 4, per my
      > diagram.
      > > > > > >
      > > > > > > Steve Spence
      > > > > > > Renewable energy and self sufficiency
      > > > > > > http://www.green- trust.org <http://www.green- trust.org
      > > > > > <http://www.green- trust.org <http://www.green- trust.org
      > > > <http://www.green- trust.org <http://www.green- trust.org
      > <http://www.green-trust.org>>>>>>
      > > > > > > http://makingtheweb work.blogspot. com/
      > > > > > > <http://makingtheweb work.blogspot. com/
      > > > > > <http://makingtheweb work.blogspot. com/
      > > > > <http://makingtheweb work.blogspot. com/
      > > > <http://makingtheweb work.blogspot. com/
      > > <http://makingtheweb work.blogspot. com/
      > <http://makingthewebwork.blogspot.com/>>>>>>
      > > > > > >
      > > > > > > sanjeev rao wrote:
      > > > > > > >
      > > > > > > >
      > > > > > > > it is 60 turns per coil 2 x 60 = 120 turns per phase,
      > > > > > > >
      > > > > > > > --coils in a phase are in series, does this means as of
      > > > > now it is
      > > > > > > > connected like this, 1-4, 2-5, 3-6
      > > > > > > >
      > > > > > > > 1-2-3 starting tip is all connected together (wye/star
      > > > > connection)
      > > > > > > >
      > > > > > > > since i am using 10" 3mm metal disc, i used only 6
      > > > > (because it was
      > > > > > > > accomadating only this much)
      > > > > > > >
      > > > > > > >
      > > > > > > >
      > > > > > > > --- On *Mon, 4/12/10, Steve Spence /<sspence@green-
      > trust.org
      > > > > > > </mc/compose? to=sspence% 40green-trust. org>>/* wrote:
      > > > > > > >
      > > > > > > >
      > > > > > > > From: Steve Spence <sspence@green- trust.org
      > > > > > > </mc/compose? to=sspence% 40green-trust. org>>
      > > > > > > > Subject: Re: [axialflux] 4.5 ACvolts/phase, but
      > slows down
      > > > > when i
      > > > > > > > connect it to rectifier
      > > > > > > > To: axialflux@yahoogrou ps.com
      > > > > > > </mc/compose? to=axialflux% 40yahoogroups. com>
      > > > > > > > Date: Monday, April 12, 2010, 5:47 PM
      > > > > > > >
      > > > > > > >
      > > > > > > >
      > > > > > > > Your phases should be in parallel, so you should be
      > seeing 13v
      > > > > > on each
      > > > > > > > phase. 60 turns per coil? 60 turns total of all
      > coils? we
      > > > > use 3
      > > > > > coils
      > > > > > > > per phase, and 35 turns per coil for a 12v machine,
      > so 105
      > > > > turns per
      > > > > > > > phase. coils in a phase are in series.
      > > > > > > >
      > > > > > > > Steve Spence
      > > > > > > > Renewable energy and self sufficiency
      > > > > > > > http://www.green- trust.org <http://www.green- trust.org
      > > > > > > <http://www.green- trust.org <http://www.green- trust.org
      > > > > <http://www.green- trust.org <http://www.green- trust.org
      > > <http://www.green- trust.org <http://www.green-trust.org>>>>>>>
      > > > > > > > http://makingtheweb work.blogspot. com/
      > > > > > > > <http://makingtheweb work.blogspot. com/
      > > > > > > <http://makingtheweb work.blogspot. com/
      > > > > > <http://makingtheweb work.blogspot. com/
      > > > > <http://makingtheweb work.blogspot. com/
      > > > <http://makingtheweb work.blogspot. com/
      > > <http://makingtheweb work.blogspot. com/
      > <http://makingthewebwork.blogspot.com/>>>>>>>
      > > > > > > >
      > > > > > > > sosweet_san wrote:
      > > > > > > > >
      > > > > > > > >
      > > > > > > > > I have successfully placed the dual rotor (12 N42
      > > > > 2"x1"x.5" per
      > > > > > > disc)
      > > > > > > > > and kept as close as possible (2mm) gap between
      > the stators'
      > > > > > > > >
      > > > > > > > > the stator contains 60 turns of 14g and 17g
      > together and
      > > > > 6 coils
      > > > > > > > overall
      > > > > > > > > in star connection (2 coils per phase)
      > > > > > > > >
      > > > > > > > > when i connected it to my low speed drill machine(500
      > > > > rpm), it
      > > > > > > > shows 4.5
      > > > > > > > > AC volts per phase, so is it 13.5 AC Volts
      > > > > > > > >
      > > > > > > > > also when i connect MB3510 per phase (SINGLE-PHASE
      > > > > SILICON BRIDGE
      > > > > > > > > RECTIFIER (VOLTAGE RANGE 50 to 1000 Volts CURRENT 35
      > > > > Amperes) the
      > > > > > > > shaft
      > > > > > > > > is experiencing somekind of slowness and it shows only
      > > > > 1.5DC volts
      > > > > > > > max,
      > > > > > > > > and stops
      > > > > > > > >
      > > > > > > > > can anyone out there help me on what could be the
      > issue
      > > > > and how
      > > > > > > it can
      > > > > > > > > be sorted out?
      > > > > > > > >
      > > > > > > > >
      > > > > > > >
      > > > > > > >
      > > > > > > >
      > > > > > >
      > > > > > >
      > > > > > >
      > > > > >
      > > > > >
      > > > > >
      > > > >
      > > > >
      > > > >
      > > > >
      > > >
      > > >
      > > >
      > >
      > >
      > >
      >
      >
      >
      >
    • sanjeev rao
      fine, let me try and will update it here. ... From: Steve Spence Subject: Re: [axialflux] 4.5 ACvolts/phase, but slows down when i
      Message 2 of 26 , May 3, 2010
      View Source
      • 0 Attachment
        fine, let me try and will update it here.

        --- On Sat, 5/1/10, Steve Spence <sspence@...> wrote:

        From: Steve Spence <sspence@...>
        Subject: Re: [axialflux] 4.5 ACvolts/phase, but slows down when i connect it to rectifier
        To: axialflux@yahoogroups.com
        Date: Saturday, May 1, 2010, 5:49 PM
















         









        Battery charging time is determined by how many ah's were removed from

        the battery, and how many amps your charger puts out. If you removed 75

        ah's from the battery, and your charger produces 25 amps, then it will

        take theoretically 3 hours to recharge. Actually it will take longer as

        charging slows as the battery fills, and it takes about 20% more ah's to

        fill than you took out due to chemistry inefficiency.



        put an amp meter (or better yet an AH meter) on your circuit so you can

        see what's happening.



        Steve Spence

        Renewable energy and self sufficiency

        http://www.green- trust.org

        http://makingtheweb work.blogspot. com/
      • sanjeev rao
        I tried connecting ammeter to determine, how much amps it produces, but immediately after connecting it, the device slows down drastically and stops in few
        Message 3 of 26 , May 3, 2010
        View Source
        • 0 Attachment
          I tried connecting ammeter to determine, how much amps it produces, but immediately after connecting it, the device slows down drastically and stops in few seconds

          what would have gone wrong?



          --- On Sat, 5/1/10, Steve Spence <sspence@...> wrote:

          From: Steve Spence <sspence@...>
          Subject: Re: [axialflux] 4.5 ACvolts/phase, but slows down when i connect it to rectifier
          To: axialflux@yahoogroups.com
          Date: Saturday, May 1, 2010, 5:49 PM

           

          Battery charging time is determined by how many ah's were removed from
          the battery, and how many amps your charger puts out. If you removed 75
          ah's from the battery, and your charger produces 25 amps, then it will
          take theoretically 3 hours to recharge. Actually it will take longer as
          charging slows as the battery fills, and it takes about 20% more ah's to
          fill than you took out due to chemistry inefficiency.

          put an amp meter (or better yet an AH meter) on your circuit so you can
          see what's happening.

          Steve Spence
          Renewable energy and self sufficiency
          http://www.green- trust.org
          http://makingtheweb work.blogspot. com/

          On 04/30/2010 06:06 AM, sanjeev rao wrote:
          >
          >
          > Good day members
          >
          > I have connected Generator and at 200 RPM it produces 24+ ACvolts/phase,
          > but when i tried connecting rectifiers it was showing me only 18+DCV, i
          > was in a impression that 24 ACV x 1.73 = DCvoltage output, but it has
          > turned up otherway
          >
          > so i tried charging my battery (10Ah 12V battery) it took almost 6 hours
          > to charge complete battery from 4.7V to 12.6 V
          >
          > then i was suspecting the battery , tried charging bike battery 2.5Ah
          > L-C , even that took close to 1 hours.
          >
          > what am i doing mistake, is the output not sufficient? not much of amps,
          >
          > configuration of stator has got changed to 250Turns #18 wires per coil
          > so per phase 500 turns of #18 wire and two coils per phase. Over all 6
          > coils providing 3 phase,
          >
          > with the help of multimeter, when i checked the Ohms it was showing
          > 2ohms for two coils connected together
          >
          > Also i noticed when i connected to 2.5 Ah battery the rotation has got
          > reduced to 70+RPM not the 200RPM
          >
          > what went wrong
          >
          >
          > --- On *Tue, 4/27/10, sanjeev rao /<sosweet_san@ yahoo.com>/* wrote:
          >
          >
          > From: sanjeev rao <sosweet_san@ yahoo.com>
          > Subject: Re: [axialflux] 4.5 ACvolts/phase, but slows down when i
          > connect it to rectifier
          > To: axialflux@yahoogrou ps.com
          > Date: Tuesday, April 27, 2010, 7:44 AM
          >
          > thats great info steve, honestly i am getting boosted by these
          > answers, surely this week i will achieve this goal and get back to you.
          >
          > because of you and fellow members like charles, i could reach, from
          > 4.5V to 24V
          >
          > thanks steve spence, charles evans
          >
          > -sanjeev
          >
          >
          > --- On *Tue, 4/27/10, Steve Spence /<sspence@green- trust.org>/* wrote:
          >
          >
          > From: Steve Spence <sspence@green- trust.org>
          > Subject: Re: [axialflux] 4.5 ACvolts/phase, but slows down when
          > i connect it to rectifier
          > To: axialflux@yahoogrou ps.com
          > Date: Tuesday, April 27, 2010, 1:11 AM
          >
          >
          >
          > I would not suggest wiring for 240. I would suggest wiring for
          > 24 or 48
          > volts, and use an inverter to get your 240vac. Then you don't
          > have to
          > worry about frequency (rpm) regulation.
          >
          > The tail of the turbine will keep voltages down, and a dump
          > controller
          > will prevent over charging.
          >
          > Steve Spence
          > Renewable energy and self sufficiency
          > http://www.green- trust.org <http://www.green- trust.org>
          > http://makingtheweb work.blogspot. com/
          > <http://makingtheweb work.blogspot. com/>
          >
          > sanjeev rao wrote:
          > >
          > >
          > > its very clear now steve,
          > >
          > > if i have to get 240 volts output, either i need to have
          > 360*10 turns or
          > > 20 coils per phase,
          > >
          > > now these coils are weighing 500grams per coil i.e 1kg per phase
          > >
          > > does this weight also make difference?
          > >
          > > also if we produce more voltage is it possible we can regulate
          > it to
          > > 12DCV or 24DCV from 36Vdcv or some high odd voltages?
          > >
          > >
          > >
          > > --- On *Sat, 4/24/10, Steve Spence /<sspence@green-
          > trust.org>/* wrote:
          > >
          > >
          > > From: Steve Spence <sspence@green- trust.org>
          > > Subject: Re: [axialflux] 4.5 ACvolts/phase, but slows down when i
          > > connect it to rectifier
          > > To: axialflux@yahoogrou ps.com
          > > Date: Saturday, April 24, 2010, 6:31 PM
          > >
          > >
          > >
          > > 24v / phase is still 24v output. the phase voltages do not add.
          > >
          > > If using 2 coils per phase, You will need to wind 120v coils.
          > if you are
          > > using 3 coils per phase, then wind 80v coils.
          > >
          > > Steve Spence
          > > Renewable energy and self sufficiency
          > > http://www.green- trust.org <http://www.green- trust.org
          > <http://www.green- trust.org>>
          > > http://makingtheweb work.blogspot. com/
          > > <http://makingtheweb work.blogspot. com/
          > <http://makingtheweb work.blogspot. com/>>
          > >
          > > sanjeev rao wrote:
          > > >
          > > >
          > > > thanks steve, as per your guidance, the device is making
          > good result,
          > > >
          > > >
          > > > now it produces 12ACV/coil , six coils in 3phases, (2per phase
          > > 180turns
          > > > of #17 / coil and per phase 360 turns,), if we have to get 240
          > > volt ac,
          > > > what would be the best approach here we need to?
          > > >
          > > > is this calculations right?
          > > >
          > > > 12 x 2 = 24ACV per phase and 72ACV
          > > >
          > > > or if we can use any other wire size like #19awg or #20awg
          > will that
          > > > make difference?
          > > >
          > > > --
          > > >
          > > >
          > > > --- On *Thu, 4/22/10, Steve Spence /<sspence@green- trust.org
          > > </mc/compose? to=sspence% 40green-trust. org>>/* wrote:
          > > >
          > > >
          > > > From: Steve Spence <sspence@green- trust.org
          > > </mc/compose? to=sspence% 40green-trust. org>>
          > > > Subject: Re: [axialflux] 4.5 ACvolts/phase, but slows down
          > when i
          > > > connect it to rectifier
          > > > To: axialflux@yahoogrou ps.com
          > > </mc/compose? to=axialflux% 40yahoogroups. com>
          > > > Date: Thursday, April 22, 2010, 4:03 PM
          > > >
          > > >
          > > >
          > > > If whatever is turning the alt (hydro, engine, whatever) has rpm
          > > > control, ie. a governor, then you will get constant output.
          > > >
          > > > Steve Spence
          > > > Renewable energy and self sufficiency
          > > > http://www.green- trust.org <http://www.green- trust.org
          > > <http://www.green- trust.org <http://www.green- trust.org>>>
          > > > http://makingtheweb work.blogspot. com/
          > > > <http://makingtheweb work.blogspot. com/
          > > <http://makingtheweb work.blogspot. com/
          > <http://makingtheweb work.blogspot. com/>>>
          > > >
          > > > sanjeev rao wrote:
          > > > >
          > > > >
          > > > > Hi again
          > > > >
          > > > > might be a stupid query, dont know how to format this query,
          > > > >
          > > > > what do i need to do if i have to get constant output from
          > this
          > > device
          > > > >
          > > > > one thing is if it is constant RPM, then it can produce
          > constant
          > > > output,
          > > > > in that case can i avoid battery banking,
          > > > >
          > > > > like a petrol generator?
          > > > >
          > > > > --sanjeev
          > > > >
          > > > > --- On *Mon, 4/19/10, sanjeev rao /<sosweet_san@ yahoo.com
          > > > </mc/compose? to=sosweet_ san%40yahoo. com>>/* wrote:
          > > > >
          > > > >
          > > > > From: sanjeev rao <sosweet_san@ yahoo.com
          > > > </mc/compose? to=sosweet_ san%40yahoo. com>>
          > > > > Subject: Re: [axialflux] 4.5 ACvolts/phase, but slows down
          > when i
          > > > > connect it to rectifier
          > > > > To: axialflux@yahoogrou ps.com
          > > > </mc/compose? to=axialflux% 40yahoogroups. com>
          > > > > Date: Monday, April 19, 2010, 6:34 AM
          > > > >
          > > > >
          > > > >
          > > > > thanks steve and Charles Evans,
          > > > >
          > > > > i am trying to achieve 700+watts at this rpm,
          > > > >
          > > > > let me start winding a new stator
          > > > >
          > > > > --- On *Mon, 4/19/10, Steve Spence /<sspence@green-
          > trust.org>/*
          > > > wrote:
          > > > >
          > > > >
          > > > > From: Steve Spence <sspence@green- trust.org>
          > > > > Subject: Re: [axialflux] 4.5 ACvolts/phase, but slows down
          > when
          > > > > i connect it to rectifier
          > > > > To: axialflux@yahoogrou ps.com
          > > > > Date: Monday, April 19, 2010, 1:43 AM
          > > > >
          > > > >
          > > > >
          > > > > I use 70 turns of 14g.
          > > > >
          > > > > Steve Spence
          > > > > Renewable energy and self sufficiency
          > > > > http://www.green- trust.org <http://www.green- trust.org
          > > > <http://www.green- trust.org <http://www.green- trust.org
          > <http://www.green- trust.org>>>>
          > > > > http://makingtheweb work.blogspot. com/
          > > > > <http://makingtheweb work.blogspot. com/
          > > > <http://makingtheweb work.blogspot. com/
          > > <http://makingtheweb work.blogspot. com/
          > <http://makingtheweb work.blogspot. com/>>>>
          > > > >
          > > > > sanjeev rao wrote:
          > > > > >
          > > > > >
          > > > > > thanks steve
          > > > > >
          > > > > > i tried with my car alternator rectifier(Denso alternator
          > > > > 12V), it shows
          > > > > > me 7.1V at DCV
          > > > > >
          > > > > > If i have to rewind the entire set of coils, and this time i
          > > > > would like
          > > > > > to go for 9 coils 12 magnets in 10" disc, for 24V how many
          > > > > turns i need
          > > > > > to wind? is there any formulae or any simple method to
          > arrive
          > > > > this turn
          > > > > > calculations?
          > > > > >
          > > > > > please help!
          > > > > >
          > > > > > --sanjeev
          > > > > >
          > > > > > --- On *Wed, 4/14/10, Steve Spence /<sspence@green-
          > > > > trust.org>/* wrote:
          > > > > >
          > > > > >
          > > > > > From: Steve Spence <sspence@green- trust.org>
          > > > > > Subject: Re: [axialflux] 4.5 ACvolts/phase, but slows
          > down when i
          > > > > > connect it to rectifier
          > > > > > To: axialflux@yahoogrou ps.com
          > > > > > Date: Wednesday, April 14, 2010, 3:48 PM
          > > > > >
          > > > > >
          > > > > >
          > > > > > I use 100 amp 600v diodes in my 3 phase rectifiers. I
          > also use
          > > > > double
          > > > > > strands of 14g for 12v units, and single strand 14g for
          > 24v units.
          > > > > >
          > > > > > Voltage is subject to the number of turns, and size of the
          > > > > coil (and
          > > > > > strength of magnet and rpm), but the inventor of this
          > > > > technology, Hugh
          > > > > > Piggott, made this determination. Doubling the number of
          > > > > turns, doubles
          > > > > > the voltage.
          > > > > >
          > > > > > Steve Spence
          > > > > > Renewable energy and self sufficiency
          > > > > > http://www.green- trust.org <http://www.green- trust.org
          > > > > <http://www.green- trust.org <http://www.green- trust.org
          > > <http://www.green- trust.org <http://www.green- trust.org>>>>>
          > > > > > http://makingtheweb work.blogspot. com/
          > > > > > <http://makingtheweb work.blogspot. com/
          > > > > <http://makingtheweb work.blogspot. com/
          > > > <http://makingtheweb work.blogspot. com/
          > > <http://makingtheweb work.blogspot. com/
          > <http://makingtheweb work.blogspot. com/>>>>>
          > > > > >
          > > > > > sanjeev rao wrote:
          > > > > > >
          > > > > > >
          > > > > > > yes this is how it is connected
          > > > > > >
          > > > > > > coils 1 & 4 in series, 2 & 5 in series, and 3 & 6
          > > > > > > in series,
          > > > > > >
          > > > > > >
          > > > > > >>>but you would need 6 diodes, not 4, per my diagram
          > > > > > >
          > > > > > > what type of diode's i need to buy?
          > > > > > >
          > > > > > > also how do you arrive 105 turns per phase will
          > produce 12v? (my
          > > > > > > apologies, is this 17g wire or 14g?)
          > > > > > > if i use 210turns will it produces 24 volts, for 48 v?
          > > > > > >
          > > > > > >
          > > > > > >
          > > > > > > --- On *Wed, 4/14/10, Steve Spence /<sspence@green-
          > trust.org
          > > > > > </mc/compose? to=sspence% 40green-trust. org>>/* wrote:
          > > > > > >
          > > > > > >
          > > > > > > From: Steve Spence <sspence@green- trust.org
          > > > > > </mc/compose? to=sspence% 40green-trust. org>>
          > > > > > > Subject: Re: [axialflux] 4.5 ACvolts/phase, but slows down
          > > > > when i
          > > > > > > connect it to rectifier
          > > > > > > To: axialflux@yahoogrou ps.com
          > > > > > </mc/compose? to=axialflux% 40yahoogroups. com>
          > > > > > > Date: Wednesday, April 14, 2010, 4:00 AM
          > > > > > >
          > > > > > >
          > > > > > >
          > > > > > > a two phase unit would have coils 1 & 3 in series, and
          > 2 & 4 in
          > > > > > series.
          > > > > > > You can't do a 2 phase with 6 coils, but only 2 in
          > series. you
          > > > > > could do
          > > > > > > a 3 phase unit, with coils 1 & 4 in series, 2 & 5 in
          > series,
          > > > > and 3 & 6
          > > > > > > in series, but you would need 6 diodes, not 4, per my
          > diagram.
          > > > > > >
          > > > > > > Steve Spence
          > > > > > > Renewable energy and self sufficiency
          > > > > > > http://www.green- trust.org <http://www.green- trust.org
          > > > > > <http://www.green- trust.org <http://www.green- trust.org
          > > > <http://www.green- trust.org <http://www.green- trust.org
          > <http://www.green- trust.org>>>>>>
          > > > > > > http://makingtheweb work.blogspot. com/
          > > > > > > <http://makingtheweb work.blogspot. com/
          > > > > > <http://makingtheweb work.blogspot. com/
          > > > > <http://makingtheweb work.blogspot. com/
          > > > <http://makingtheweb work.blogspot. com/
          > > <http://makingtheweb work.blogspot. com/
          > <http://makingtheweb work.blogspot. com/>>>>>>
          > > > > > >
          > > > > > > sanjeev rao wrote:
          > > > > > > >
          > > > > > > >
          > > > > > > > it is 60 turns per coil 2 x 60 = 120 turns per phase,
          > > > > > > >
          > > > > > > > --coils in a phase are in series, does this means as of
          > > > > now it is
          > > > > > > > connected like this, 1-4, 2-5, 3-6
          > > > > > > >
          > > > > > > > 1-2-3 starting tip is all connected together (wye/star
          > > > > connection)
          > > > > > > >
          > > > > > > > since i am using 10" 3mm metal disc, i used only 6
          > > > > (because it was
          > > > > > > > accomadating only this much)
          > > > > > > >
          > > > > > > >
          > > > > > > >
          > > > > > > > --- On *Mon, 4/12/10, Steve Spence /<sspence@green-
          > trust.org
          > > > > > > </mc/compose? to=sspence% 40green-trust. org>>/* wrote:
          > > > > > > >
          > > > > > > >
          > > > > > > > From: Steve Spence <sspence@green- trust.org
          > > > > > > </mc/compose? to=sspence% 40green-trust. org>>
          > > > > > > > Subject: Re: [axialflux] 4.5 ACvolts/phase, but
          > slows down
          > > > > when i
          > > > > > > > connect it to rectifier
          > > > > > > > To: axialflux@yahoogrou ps.com
          > > > > > > </mc/compose? to=axialflux% 40yahoogroups. com>
          > > > > > > > Date: Monday, April 12, 2010, 5:47 PM
          > > > > > > >
          > > > > > > >
          > > > > > > >
          > > > > > > > Your phases should be in parallel, so you should be
          > seeing 13v
          > > > > > on each
          > > > > > > > phase. 60 turns per coil? 60 turns total of all
          > coils? we
          > > > > use 3
          > > > > > coils
          > > > > > > > per phase, and 35 turns per coil for a 12v machine,
          > so 105
          > > > > turns per
          > > > > > > > phase. coils in a phase are in series.
          > > > > > > >
          > > > > > > > Steve Spence
          > > > > > > > Renewable energy and self sufficiency
          > > > > > > > http://www.green- trust.org <http://www.green- trust.org
          > > > > > > <http://www.green- trust.org <http://www.green- trust.org
          > > > > <http://www.green- trust.org <http://www.green- trust.org
          > > <http://www.green- trust.org <http://www.green- trust.org>>>>>>>
          > > > > > > > http://makingtheweb work.blogspot. com/
          > > > > > > > <http://makingtheweb work.blogspot. com/
          > > > > > > <http://makingtheweb work.blogspot. com/
          > > > > > <http://makingtheweb work.blogspot. com/
          > > > > <http://makingtheweb work.blogspot. com/
          > > > <http://makingtheweb work.blogspot. com/
          > > <http://makingtheweb work.blogspot. com/
          > <http://makingtheweb work.blogspot. com/>>>>>>>
          > > > > > > >
          > > > > > > > sosweet_san wrote:
          > > > > > > > >
          > > > > > > > >
          > > > > > > > > I have successfully placed the dual rotor (12 N42
          > > > > 2"x1"x.5" per
          > > > > > > disc)
          > > > > > > > > and kept as close as possible (2mm) gap between
          > the stators'
          > > > > > > > >
          > > > > > > > > the stator contains 60 turns of 14g and 17g
          > together and
          > > > > 6 coils
          > > > > > > > overall
          > > > > > > > > in star connection (2 coils per phase)
          > > > > > > > >
          > > > > > > > > when i connected it to my low speed drill machine(500
          > > > > rpm), it
          > > > > > > > shows 4.5
          > > > > > > > > AC volts per phase, so is it 13.5 AC Volts
          > > > > > > > >
          > > > > > > > > also when i connect MB3510 per phase (SINGLE-PHASE
          > > > > SILICON BRIDGE
          > > > > > > > > RECTIFIER (VOLTAGE RANGE 50 to 1000 Volts CURRENT 35
          > > > > Amperes) the
          > > > > > > > shaft
          > > > > > > > > is experiencing somekind of slowness and it shows only
          > > > > 1.5DC volts
          > > > > > > > max,
          > > > > > > > > and stops
          > > > > > > > >
          > > > > > > > > can anyone out there help me on what could be the
          > issue
          > > > > and how
          > > > > > > it can
          > > > > > > > > be sorted out?
          > > > > > > > >
          > > > > > > > >
          > > > > > > >
          > > > > > > >
          > > > > > > >
          > > > > > >
          > > > > > >
          > > > > > >
          > > > > >
          > > > > >
          > > > > >
          > > > >
          > > > >
          > > > >
          > > > >
          > > >
          > > >
          > > >
          > >
          > >
          > >
          >
          >
          >
          >


        Your message has been successfully submitted and would be delivered to recipients shortly.