Re: [Distillers] copper heating elements!

Expand Messages
  • Martin
    Is this RCD the same device that I know as an Earth Leakage Unit ?
    Message 1 of 29 , Jun 1, 2003
    • 0 Attachment
      Is this RCD the same device that I know as an "Earth Leakage Unit"?
    • Allan Goldsmith
      yep Allan ... From: Martin To: Distillers@yahoogroups.com Sent: Monday, June 02, 2003 12:35 PM Subject: Re: [Distillers] copper heating elements! Is this RCD
      Message 2 of 29 , Jun 1, 2003
      • 0 Attachment
        yep
        Allan
        ----- Original Message -----
        From: Martin
        Sent: Monday, June 02, 2003 12:35 PM
        Subject: Re: [Distillers] copper heating elements!

        Is this RCD the same device that I know as an "Earth Leakage Unit"?


        To unsubscribe from this group send a blank email to   distillers-unsubscribe@yahoogroups.com
        Distillers list archives : http://archive.nnytech.net/
        FAQ and other information at http://homedistiller.org


        Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.
      • Harley Daschund
        RCD/...is that like a GFCI (USA) ?...wouldnt run my stills on anything else...: ) ... _________________________________________________________________ Protect
        Message 3 of 29 , Jun 1, 2003
        • 0 Attachment
          RCD/...is that like a GFCI (USA) ?...wouldnt run my stills on anything
          else...:>)


          >From: "Ackland, Tony (CALNZAS)" <Tony.Ackland@...>
          >Reply-To: Distillers@yahoogroups.com
          >To: <Distillers@yahoogroups.com>
          >Subject: RE: [Distillers] copper heating elements!
          >Date: Mon, 2 Jun 2003 11:49:31 +1200
          >
          > > there IS a significant safety issue with tinned copper heating
          > > elements. Not copper in the wash, but pinhole corrosion through the
          > > copper sheath, leading to a dead short circuit, which could lead to
          > > runaway heating of the wash, an electrically "hot" boiler, and of
          > > course, a blown fuse or breaker.
          >
          >Yep ! Gives a nice bang too when it happens. Guess why I'm such a strong
          >advocate for using RCD's whenever theres a combination of electricity and
          >liquid about.
          >
          >Tony

          _________________________________________________________________
          Protect your PC - get McAfee.com VirusScan Online
          http://clinic.mcafee.com/clinic/ibuy/campaign.asp?cid=3963
        • Aaron Pelly
          i think your name is the correct one martin. the device does indeed detect earth leakage. ... From: Martin [mailto:martinmarburger@shaw.ca] Sent: 02 June 2003
          Message 4 of 29 , Jun 1, 2003
          • 0 Attachment
            i think your name is the correct one martin. the device does indeed detect earth leakage.
            -----Original Message-----
            From: Martin [mailto:martinmarburger@...]
            Sent: 02 June 2003 12:36
            To: Distillers@yahoogroups.com
            Subject: Re: [Distillers] copper heating elements!

            Is this RCD the same device that I know as an "Earth Leakage Unit"?
          • BOKAKOB
            Mike, thank you for explanations. I wonder what is the column working primary downward? and how it is working? Thsnks in advance, Alex... mwmccaw
            Message 5 of 29 , Jun 2, 2003
            • 0 Attachment
              Mike, thank you for explanations. I wonder what is the column working primary downward? and how it is working? Thsnks in advance, Alex...

              mwmccaw <mwmccaw@...> wrote:
              Now a pair of continuous columns, one operating primarily upwards, and one operating primarily downwards, in series could theoretically separate the ethanol and heads from everything else, then separate
              the heads from the ethanol.
              Mike McCaw


              Do you Yahoo!?
              Free online calendar with sync to Outlook(TM).
            • mwmccaw
              And in the US, they re knows as a Ground Fault Circuit Interrupter device. MM ... Unit ? ... distillers-unsubscribe@yahoogroups.com ... Service.
              Message 6 of 29 , Jun 2, 2003
              • 0 Attachment
                And in the US, they're knows as a "Ground Fault Circuit Interrupter"
                device.
                MM

                --- In Distillers@yahoogroups.com, "Allan Goldsmith"
                <goldsmith@w...> wrote:
                > yep
                > Allan
                > ----- Original Message -----
                > From: Martin
                > To: Distillers@yahoogroups.com
                > Sent: Monday, June 02, 2003 12:35 PM
                > Subject: Re: [Distillers] copper heating elements!
                >
                >
                > Is this RCD the same device that I know as an "Earth Leakage
                Unit"?
                >
                > Yahoo! Groups Sponsor
                > ADVERTISEMENT
                >
                >
                >
                >
                > To unsubscribe from this group send a blank email to
                distillers-unsubscribe@yahoogroups.com
                > Distillers list archives : http://archive.nnytech.net/
                > FAQ and other information at http://homedistiller.org
                >
                > Your use of Yahoo! Groups is subject to the Yahoo! Terms of
                Service.
              • mwmccaw
                Sorry, Alex - What I was describing was the path that the ethanol follows in the two serial columns. In the first column, heated by steam from below, the wash
                Message 7 of 29 , Jun 2, 2003
                • 0 Attachment
                  Sorry, Alex -
                  What I was describing was the path that the ethanol follows in the
                  two serial columns.
                  In the first column, heated by steam from below, the wash enters in
                  the middle, and water and tails go out the bottom and ethanol and
                  heads go out the top.
                  The ethanol and heads now go to a second column, heated by ethanol
                  vapor from below, and if it is long enough and well enough
                  controlled, the heads exit the top and the ethanol (azeotrope,
                  actually, of course)exits the bottom.
                  MM

                  --- In Distillers@yahoogroups.com, BOKAKOB <bokakob@y...> wrote:
                  > Mike, thank you for explanations. I wonder what is the column
                  working primary downward? and how it is working? Thsnks in advance,
                  Alex...
                  >
                  > mwmccaw <mwmccaw@y...> wrote:Now a pair of continuous columns, one
                  operating primarily upwards, and one operating primarily downwards,
                  in series could theoretically separate the ethanol and heads from
                  everything else, then separate
                  > the heads from the ethanol.
                  > Mike McCaw
                  >
                  >
                  > ---------------------------------
                  > Do you Yahoo!?
                  > Free online calendar with sync to Outlook(TM).
                • Robert Lougee
                  Also known as a GFI or Ground Fault Interrupt in the USA. Particularly usefull in the bathroom or kitchen. If an appliance plugged into the GFI falls in the
                  Message 8 of 29 , Jun 2, 2003
                  • 0 Attachment
                    Also known as a GFI or Ground Fault Interrupt in the USA. Particularly
                    usefull in the bathroom or kitchen. If an appliance plugged into the
                    GFI falls in the water, it trips to stop current flow and avoid
                    electrocution.

                    "If it pours, drink it."
                    Robert

                    --- In Distillers@yahoogroups.com, "Allan Goldsmith" <goldsmith@w...>
                    wrote:
                    > yep
                    > Allan
                    > ----- Original Message -----
                    > From: Martin
                    > To: Distillers@yahoogroups.com
                    > Sent: Monday, June 02, 2003 12:35 PM
                    > Subject: Re: [Distillers] copper heating elements!
                    >
                    >
                    > Is this RCD the same device that I know as an "Earth Leakage
                    Unit"?
                    >
                    > Yahoo! Groups Sponsor
                    > ADVERTISEMENT
                    >
                    >
                    >
                    >
                    > To unsubscribe from this group send a blank email to distillers-
                    unsubscribe@yahoogroups.com
                    > Distillers list archives : http://archive.nnytech.net/
                    > FAQ and other information at http://homedistiller.org
                    >
                    > Your use of Yahoo! Groups is subject to the Yahoo! Terms of
                    Service.
                  • Ken Grady
                    As someone from Oz has already stated they are called earth leakage switches here & are compulsory to be installed in all new homes for the the last 10 years.
                    Message 9 of 29 , Jun 2, 2003
                    • 0 Attachment
                       
                      As someone from Oz has already stated they are called earth leakage switches  here & are compulsory to be installed in all new homes for the the last 10 years.
                       
                      Ken.
                       
                       
                      Also known as a GFI or Ground Fault Interrupt in the USA. Particularly
                      usefull in the bathroom or kitchen. If an appliance plugged into the
                      GFI falls in the water, it trips to stop current flow and avoid
                      electrocution.

                      "If it pours, drink it."
                      Robert

                    • rodmacd2000
                      I assume an RCD is the same thing we in N. America would call a GFD (Ground Fault Detector)? I question the need for such a device in the case when your boiler
                      Message 10 of 29 , Jun 3, 2003
                      • 0 Attachment
                        I assume an RCD is the same thing we in N. America would call a GFD
                        (Ground Fault Detector)?

                        I question the need for such a device in the case when your boiler is
                        a properly grounded vessel such as a correctly wired hot water heater.

                        --- In Distillers@yahoogroups.com, "Allan Goldsmith" <goldsmith@w...>
                        wrote:
                        > RCDs are residual current devices. they trip when the difference in
                        current going through neutral is not equal to the current on phase.
                        (therefore going through your body..eeek)
                        > usually trip at 30 -70 mA in a few microseconds so your heart
                        doesn't stop.
                        > Used in Aus for the first time I believe in the ABBA concert which
                        was held in Sydney in the pouring rain. May be wrong here.
                        > cheers
                        > Allan
                        > ----- Original Message -----
                        > From: Martin
                        > To: distillers@yahoogroups.com
                        > Sent: Monday, June 02, 2003 12:13 PM
                        > Subject: Re: [Distillers] copper heating elements!
                        >
                        >
                        > Tony,
                        >
                        > Please explain what you mean by an "RCD".
                        >
                        > Martin
                        >
                        > Yahoo! Groups Sponsor
                        >
                        >
                        >
                        > To unsubscribe from this group send a blank email to distillers-
                        unsubscribe@yahoogroups.com
                        > Distillers list archives : http://archive.nnytech.net/
                        > FAQ and other information at http://homedistiller.org
                        >
                        > Your use of Yahoo! Groups is subject to the Yahoo! Terms of
                        Service.
                      • Ackland, Tony (CALNZAS)
                        ... Yes ... Incase of accidents - eg the element shorting out, or wires fraying or getting crimped in something (like a door), or liquid spills out over the
                        Message 11 of 29 , Jun 3, 2003
                        • 0 Attachment
                          > I assume an RCD is the same thing we in N. America would call a GFD
                          > (Ground Fault Detector)?

                          Yes

                          > I question the need for such a device in the case when your boiler is
                          > a properly grounded vessel such as a correctly wired hot water heater.

                          Incase of accidents - eg the element shorting out, or wires fraying or getting crimped in something (like a door), or liquid spills out over the wiring somehow ... I'm sure you can dream up a scenario. At work, we have mandated that all power points (plug-in and permanent) are to have RCD protection, just for the backup safety they offer. And there have been enough close calls to have made it a wise call. Note that they dont prevent you from getting an electric shock, but hopefully reduce its severity & duration so that it is no longer as dangerous.

                          For me at home its important because my boiler is portable, and not grounded.

                          Tony